<DIV><FONT size=2 face=Arial>I agree with Kelly and others that all grounding 
electrodes should be bonded together. My experience in lightning country 
with PV systems with a ground rod at the array and separate ground rod 
at the BOS and no wire connecting  the ground rods has always resulted 
in fried equipment. The same systems, after they were repaired and the ground 
rods were connected together, survived every lightning storm for several 
years. I have found that the same holds true for any equipment or 
structure - good earth grounds all connected together create a grounding field 
and can create a cone of protection. Properly grounded equipment with all 
grounding electrodes connected together generally survive lightning storms 
and have been known to survive direct lightning strikes.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Joel Davidson</FONT></DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=bcrise@nietc.org href="mailto:bcrise@nietc.org">Brian Crise</A> 
</DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Friday, June 05, 2009 1:45 PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] 690.47D 
  (revisited)</DIV>
  <DIV><BR></DIV>Kelly,
  <DIV>It is my understanding that all types of grounding electrodes, 
  whether supplementary or not, for lightning protection or PV array 
  grounding shall be bonded together to form the grounding electrode system. 
  (250.106, 690.47(A) which sends you to 250.50,   NFPA 780-2008 4.14). 
   If you do not do this and you do get a lightning strike or for 
  that matter any high frequency signal injected onto a grounding electrode you 
  will get what they call a ground potential rise onto one part of the system. 
   With the other separate grounding electrode not having this 
  same signal because of them not being common, you will have a 
  potential difference between the two separate electrodes even though 
  they are both in the ground.  The ground (earth) is actually a very poor 
  conductor when it comes to high levels of high frequency current</DIV>
  <DIV>Hopefully this helps,</DIV>
  <DIV>Brian</DIV>
  <DIV><BR></DIV>
  <DIV>NABCEP Certified PV Installer</DIV>
  <DIV><BR></DIV>
  <DIV>To contact Brian L Crise:</DIV>
  <DIV>
  <DIV apple-content-edited="true"><SPAN 
  style="WIDOWS: 2; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; BORDER-COLLAPSE: separate; FONT: 12px Helvetica; WHITE-SPACE: normal; ORPHANS: 2; LETTER-SPACING: normal; COLOR: rgb(0,0,0); WORD-SPACING: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0" 
  class=Apple-style-span>
  <DIV 
  style="WORD-WRAP: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space"><SPAN 
  style="WIDOWS: 2; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; BORDER-COLLAPSE: separate; FONT: 12px Helvetica; WHITE-SPACE: normal; ORPHANS: 2; LETTER-SPACING: normal; COLOR: rgb(0,0,0); WORD-SPACING: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto" 
  class=Apple-style-span>
  <DIV 
  style="WORD-WRAP: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space">
  <P style="MARGIN: 0px; MIN-HEIGHT: 14px; FONT: 12px Helvetica"><BR></P>
  <P style="MARGIN: 0px"><FONT style="FONT: 12px Helvetica" size=3 
  face=Helvetica>Address:</FONT></P>
  <P style="MARGIN: 0px"><FONT style="FONT: 12px Helvetica" size=3 
  face=Helvetica>16021 NE Airport Way</FONT></P>
  <P style="MARGIN: 0px"><FONT style="FONT: 12px Helvetica" size=3 
  face=Helvetica>Portland OR, 97230</FONT></P>
  <P style="MARGIN: 0px; MIN-HEIGHT: 14px; FONT: 12px Helvetica"><BR></P>
  <P style="MARGIN: 0px"><FONT style="FONT: 12px Helvetica" size=3 
  face=Helvetica>Office Phone:<SPAN class=Apple-converted-space><SPAN 
  class=Apple-converted-tab>   <SPAN 
  class=Apple-converted-space> </SPAN></SPAN></SPAN>(503) 262-9991 
  x.5054</FONT></P>
  <P style="MARGIN: 0px"><BR></P>
  <P style="MARGIN: 0px"><FONT style="FONT: 12px Helvetica" size=3 
  face=Helvetica>e-mail:<SPAN class=Apple-converted-space><SPAN 
  class=Apple-converted-tab>   <SPAN 
  class=Apple-converted-space> </SPAN></SPAN></SPAN><A 
  href="mailto:bcrise@nietc.org">bcrise@nietc.org</A></FONT></P></DIV><BR 
  class=Apple-interchange-newline></SPAN></DIV></SPAN><BR 
  class=Apple-interchange-newline></DIV><BR>
  <DIV>
  <DIV>On Jun 5, 2009, at 12:10 PM, Kelly Keilwitz, Whidbey Sun & Wind 
  wrote:</DIV><BR class=Apple-interchange-newline>
  <BLOCKQUOTE type="cite">
    <DIV>Mark, <BR>I don't think that the 690.47D "PV GE" is part of the 
    premises AC & DC<BR>ground electrode system.<BR><BR>IMO, in order to 
    function to properly as “enhanced protection from lightning<BR>induced 
    surges” as described in the 690.47(D) section note in the 2008 
    NEC<BR>Handbook, the “optional supplementary grounding electrode” should not 
    be<BR>connected to the premises system AC and DC grounding electrodes, as 
    shown in<BR>Exhibit 690.6 of the Handbook. If an additional #8 (per 250.166) 
    is bonded<BR>to the premises AC/DC system GE, it's path will be parallel 
    with, and<BR>redundant to, the existing EGC. This could set up the potential 
    for an<BR>inductive ground loop, which might cause more damage to the system 
    during a<BR>lightning strike than it would prevent.<BR><BR>If the 
    “additional electrode for array grounding” (PV GE) of 690.47D is 
    not<BR>required, then the PV GEC of that section should not be 
    required.<BR><BR>Of course, these opinions are academic. What I really want 
    to know is what<BR>the AHJ's think! Any of you have to deal with this, 
    yet?<BR><BR>Thanks,<BR>-Kelly<BR><BR>Kelly Keilwitz, P.E.<BR>Whidbey Sun 
    & Wind, LLC<BR>Renewable Energy Systems<BR>NABCEP Certified PV 
    Installer<BR>WA Electrical Administrator #KEILWKM923RB<BR>987 Wanamaker 
    Rd.<BR>Coupeville, WA, 98239<BR>360.678.7131<BR><A 
    href="mailto:sunwind@whidbeysunwind.com">sunwind@whidbeysunwind.com</A><BR>WA 
    Electrical Contractor #WHIDBSW920MS<BR>WA General Contractor 
    #WHIDBSW946M1<BR><BR><BR><BR><BR>On 6/5/09 10:01 AM, "Mark Frye" 
    <markf@berkeleysolar.com> wrote:<BR><BR>
    <BLOCKQUOTE type="cite">Kelly,<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">The question is, if the AJH had required you to 
      run the new array DC GEC<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">directly to an additional DC array GE, would that 
      new DC GE system need to<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">be bonded with the exisitng AC GE system with a 
      bonding wire other than the<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">new EGC running from the array to new DC 
    GE?<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">Unfortunately, NEC 2008 is not clear about this 
      with respect to the new DC<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">array GE.  That leaves us with only the 
      general NEC requirement that all<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">premise GE's be bonded into a single 
    system.<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">So the total effect of the new 690.47D, assuming 
      that the "prcaticable"<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">location for the new DC array GE is not within 6 
      ft of the exisiting AC GE,<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">is this:<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">A new DC array GEC must run directly from the 
      array to a new DC GE system<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">and and a new bonding jumper must be run from the 
      new DC GE system to the<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">exisitng AC GE system.<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">It the new DC GE system can be the same as the 
      existing AC GE by virtue of<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">it proximity (less than 6 ft) to the practiable 
      location, then the ne DC<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">array GEC must still be run directly to exist GE 
      system which is now the<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">AC/DC GE system.<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">Mark Frye<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">Berkeley Solar Electric Systems<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">303 Redbud Way<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">Nevada City,  CA 95959<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">(530) 401-8024<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">www.berkeleysolar.com<BR></BLOCKQUOTE>
    <BLOCKQUOTE 
    type="cite"><BR></BLOCKQUOTE><BR><BR>_______________________________________________<BR>List 
    sponsored by Home Power magazine<BR><BR>List Address: 
    RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
    settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
    rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
    participant 
  bios:<BR>www.members.re-wrenches.org<BR><BR></DIV></BLOCKQUOTE></DIV><BR></DIV>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>