<DIV style="font-family:Arial, sans-serif; font-size:10pt;"><DIV>Although we have completed tons of grid-tie systems, and off-grid battery systems, this will be our first AC coupled system and there are still a few things we need to resolve.  We will be using a 4 kW Sunny Island on a ground-mounted array about 150 feet from home.  We are considering using a Xantrex XW6048 since we have both a grid connection and a backup generator and thought this would be easier since everything will be 120/240 VAC except Sunny Island.  We will use a 120/240 Outback transformer to match the Sunny Island to the 240 volt hardware.</DIV>
<DIV> </DIV>
<DIV>Here are the issues that we are having a problem:</DIV>
<DIV> </DIV>
<DIV>1.  Is this inverter match up the best since we have the 240 VAC grid, 240 VAC generator, and a 240 VAC well pump on the back up panel? My concern with the Sunny Island is it may require added issues with trying to connect to two sources of AC power. </DIV>
<DIV> </DIV>
<DIV>2.  I know the Sunny Island "communicates" with the Sunny Boy by altering ithe grid frequency it sees, but I am concerned this type of control may not shut down the SunnyBoy when it sees power from the generator and will still need a isolation relay.  Is this a valid concern?</DIV>
<DIV> </DIV>
<DIV>3.  Looks like we will be in the 35 amp @ 120 VAC from the Sunny Island back-feeding the backup power panel.  Should we have the "relay" to dis-connect the SunnyBoy when the grid is down and the battery is full, or to avoid backfeed into the generator when the grid is down, but what "relay"?  Is there a specific model or size most of you are using, or do we need a contactor instead of a "relay" ?  What relay?</DIV>
<DIV> </DIV>
<DIV>4.  Do we need to run any control wiring out to the ground mounted array and remote SunnyBoy to "signal" when we are dis-connecting it from the system during the above conditions?  I have installed some inverter brands that were factory programmed to shut down when they exceed so many of the same type outage condition "errors"  thinking there was some kind of system problem. </DIV>
<DIV> </DIV>
<DIV>Thanks for the help,</DIV>
<DIV> </DIV>
<DIV>Jeff Yago</DIV><BR> <BR><HR>Netscape.  Just the Net You Need.</DIV>