color=#0000ff size=2>He may have been refering to the California Electric 
Code.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=140091513-23042009></SPAN> <BR><SPAN 
lang=en-us><FONT face=Arial size=2>Mark Frye</FONT></SPAN> <BR><SPAN 
lang=en-us><FONT face=Arial size=2>Berkeley Solar Electric Systems</FONT></SPAN> 
<BR><SPAN lang=en-us><FONT face=Arial size=2>303 Redbud Way</FONT></SPAN> 
<BR><SPAN lang=en-us><FONT face=Arial size=2>Nevada City,  CA 
95959</FONT></SPAN> <BR><SPAN lang=en-us><FONT face=Arial size=2>(530) 
401-8024</FONT></SPAN> <BR><SPAN lang=en-us></SPAN><A 
href="http://www.berkeleysolar.com/"><SPAN lang=en-us><U><FONT face=Arial 
color=#0000ff size=2>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN 
lang=en-us><FONT face=Arial size=2> </FONT></SPAN> </DIV>
<DIV> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>Nick 
Vida<BR><B>Sent:</B> Wednesday, April 22, 2009 10:04 PM<BR><B>To:</B> 
re-wrenches@lists.re-wrenches.org<BR><B>Cc:</B> 
nickvida@ymail.com<BR><B>Subject:</B> [RE-wrenches] Santa Monica guidlines/ 
CEC<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman,new york,times,serif">
<DIV>Wrenches,<BR><BR>This is an interesting email i received today from an 
inspector in Santa Monica, CA. He reference the CEC, and I am not familiar. Is 
this the Canadian Electrical Code(CEC)? <BR><BR>Also, <BR>Santa Monica, CA just 
published their guidelines and there is a link in the email. They are pretty 
close to the one Bil Brooks worked on for Schwarzenegger. <BR><BR>
<HR style="WIDTH: 100%; HEIGHT: 2px">
<BR>Here is the Email (my draft of my response follows):<BR><BR>Hi 
Nick<BR><BR>It is my understanding that your permit will be extended by 6 
months.<BR><BR>Here is the short cut for the SM PV standards.<BR><BR>Shortcut 
to:<BR><A href="http://www.qcode.us/codes/santamonica/index.php?topic=8-8_40" 
target=_blank>http://www.qcode.us/codes/<WBR>santamonica/index.php?topic=8-<WBR>8_40</A><BR><BR>Weather 
and sunlight resistant stickers are acceptable.<BR><BR><BR>The following 
correction items are in commonly overlooked.<BR>*       The PV 
source and PV output circuits can not be contained in the<BR>same raceways per 
690.4(B).<BR>*       A newer and commonly missed requirement is 
the identification of<BR>conductors of different systems. The conductors of the 
DC are required<BR>to be identified differently per 2007 CEC 310.12, 215.12, 
210.5(C) and<BR>200.6. The 2007 CEC is based on the 2005 NEC.<BR>*     
  Please download the CalOSHA requirements for the installation 
of<BR>ladders.  Inspectors will not climb ladders that are not compliant 
with<BR>the requirements.  Please be prepared to install a suitable 
ladder,<BR>inspectors may not be permitted adequate time to wait for 
the<BR>installation of various ladders.<BR><BR>If I can be of further help 
please don't hesitate to contact me.  Thanks<BR><BR><BR>Nick 
Katsenis<BR>Combination Building Inspector<BR>1685 Main Street<BR>Santa Monica, 
CA 90401<BR><BR>310.458.2201 ext.8120<BR>310.458.2104 Fax<BR><FONT 
color=#888888><A 
href="mailto:nicholas.katsenis@smgov.net">nicholas.katsenis@smgov.net</A><BR><BR></FONT>
<HR style="WIDTH: 100%; HEIGHT: 2px">
<FONT color=#888888><BR></FONT>my response draft is:<BR><BR>Nick-<BR><BR>The 
following correction items are in commonly overlooked.<BR>> 
*       The PV source and PV output circuits can 
not be contained in the<BR>> same raceways per 690.4(B).<BR><BR>the rest of 
the sentence you are referencing is:<BR><BR>"as feeder or branch circuits of 
other systems..."<BR><BR>The clarification note in the handbook is:<BR><BR>For 
example, 690.4(B) does not permit the conductors supplying an exterior lighting 
fixture located in close proximity of a roof- mounted PV array to be installed 
in the same raceway or cable with the conductors of PV source circuits or PV 
output circuits.<BR>Conductores directly related to a specific PV system, such 
as those in dc and ac output power circuits, may be contained in the same 
raceway as PV source and output conductors... (page 1020 2005 NEC 
Handbook)<BR><BR>We would only be running the solar circuits in our raceways 
connecting different runs to our gear. Are you saying you have a concern about 
such a raceway?<BR><BR>Nick Vida <BR><BR><BR>