<font size=3>Jon:<br><br>
1. Outback inverters are notorious for reporting errors
incorrectly. Often the errors are a clue, but not the actual error.
As an example, a shorted AC output might report a "Low Battery
Voltage" error because when the output is shorted, the battery draw
is momentarily very high, reducing it's voltage. Look for a related
symptom.<br><br>
Have you been able to monitor the AC voltage during inverter sell
operation? High AC voltage in a grid-tie system can be caused by
actual, intermittent high grid voltage and/or inadequate feeder size,
allowing the inverter to push up the voltage at the inverter end of the
feeder. I've seen a bad breaker cause this as well. In any of
these described cases, the inverter error reporting would be
accurate.<br><br>
2. Outback sends out a standard kit of three field-replaceable
boards. You rarely need to replace all of the boards. You
need to figure out which board(s) to replace or, ask tech support.
I guess when in doubt, one could replace all three. It appears you
have narrowed the problem down to not one of the three boards.<br><br>
Good luck.<br><br>
William Miller<br><br>
<br><br>
<br>
At 08:28 PM 4/9/2009, you wrote:<br>
<blockquote type=cite class=cite cite>I have a customer with an Outback
GTFX 3048 that has an"over voltage <br>
AC in" warning but when I check the voltage with my Fluke meter
it <br>
shows a normal range 122 - 126 V . In the Mate grid menu the AC
high <br>
Volts is set at 140 V . The customer called Outback support before
I <br>
could get to him and they told him he needed to have me change all
3 <br>
boards out. They sent the boards so I went ahead and changed them
<br>
out, but the same error occurred again. We called Outback support
<br>
again but did not get a satisfactory answer on how to fix it.<br><br>
Has anyone else run into this problem ? I suspect the Mate may be
flaky.<br><br>
Jon<br><br>
Jon Haeme Innovations<br>
Kempton, IL