Hi Darryl,<br>
<br>
Just to see what your take would be, and other's - what would the case
be should the modules have non-conducting frames (or even no frames)is
the case with some systems on the market?<br>
<br>
Matt T<br>
<br>
Darryl Thayer wrote:
<blockquote cite="mid222739.3029.qm@web51904.mail.re2.yahoo.com"
 type="cite">
  <pre wrap="">Yes the electric power and atmospheric grounding systems should be connected together to serve as a larger better grounding system.  The Electrical code requires that at only one point does the neutral (grounded) conductor of the electrical power system get connected to the grounding system, this is to prevent the grounding electrode system from carrying electrical power system currents.  The electrical power system is to be grounded to prevent the electrical power system from differentiating its self via the injection of energy from other electric power sources including atmospheric electrical energy.    
 

The lightening protection system is to create a path from the atmospheric energy to the earth grounding system.  ((Wind rain, dust and friction cause the atmosphere to become charged relative to the earth, conducting objects can build a charge if not electrically connected to the earth, these current flow all the time, although they are small sometimes, and in the case of a lightening strike incredibly large.  Even small currents can build large voltages and fail electronic components.  

The frames of solar modules are electrical conduction components not normally charged that can present a personal, and physical damage potential (life-property) if they become charged by the electrical power system and therefor the underwriters require they be protected by grounding.  This accidental energy need to be safely returned to the electrical power system, and properly this is called bonding back to the neutral conductor.  This grounding is described by the NEC in 690 and 250 primarily.   The frames of the modules can become charged by atmospheric energy energy, this energy needs to be returned to the earth, via the lightening protection system, ie grounding electrode system.  The code says little about this, however, it is addressed in 690 and 250.  

Sorry I said so much.
Darryl        


--- On Fri, 3/6/09, Drake Chamberlin <a class="moz-txt-link-rfc2396E" href="mailto:drake.chamberlin@redwoodalliance.org"><drake.chamberlin@redwoodalliance.org></a> wrote:

  </pre>
  <blockquote type="cite">
    <pre wrap="">From: Drake Chamberlin <a class="moz-txt-link-rfc2396E" href="mailto:drake.chamberlin@redwoodalliance.org"><drake.chamberlin@redwoodalliance.org></a>
Subject: Re: [RE-wrenches] Lightning protection system
To: "RE-wrenches" <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org"><re-wrenches@lists.re-wrenches.org></a>
Date: Friday, March 6, 2009, 8:47 AM
I didn't get a reply to the question about connecting
the GEC to the 
lightning protection system on the 8 story building. 
Although this 
may seem like an intrinsically dangerous idea, a lightning
protection 
system is required to be bonded to the building grounding
electrode system.

"250.106 Lightning Protection Systems.
The lightning protection system ground terminals shall be
bonded to 
the building or structure grounding electrode system."

It would therefore seem that the suplemental ground could
connect to 
that system as well, and in fact use the existing
conductor.  Any 
input would be welcome.

Thanks,

Drake




At 09:19 PM 3/4/2009, you wrote:
    </pre>
    <blockquote type="cite">
      <pre wrap="">Hello Wrenches,

Can the supplemental grounding electrode conductor be
      </pre>
    </blockquote>
    <pre wrap="">connected to a 
    </pre>
    <blockquote type="cite">
      <pre wrap="">lightning protection system?

We have a case where it would be difficult to run a GEC
      </pre>
    </blockquote>
    <pre wrap="">down a multi 
    </pre>
    <blockquote type="cite">
      <pre wrap="">story building, but have a convenient copper wire, from
      </pre>
    </blockquote>
    <pre wrap="">a lightning 
    </pre>
    <blockquote type="cite">
      <pre wrap="">protection system, that runs to a rod.

Thank you,

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648


_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: 
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

      </pre>
    </blockquote>
    <pre wrap="">Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648  


_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
    </pre>
  </blockquote>
  <pre wrap=""><!---->


      
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
  </pre>
  <pre wrap="">
<hr size="4" width="90%">

No virus found in this incoming message.
Checked by AVG - <a class="moz-txt-link-abbreviated" href="http://www.avg.com">www.avg.com</a> 
Version: 8.0.237 / Virus Database: 270.11.9/1990 - Release Date: 03/08/09 17:17:00

  </pre>
</blockquote>
</body>
</html>