<font size=3>Jeff:<br><br>
Can your client maintain batteries?<br><br>
The IBE 85N-13 is 627 AH of FLA.  One string is too small, two
strings is too large, so you may need to keep looking.  I would add
that we have had only one failure in 20 plus years of use.<br><br>
The MK-8A8DLTP  Deka is 245 amp hours of AGM.  Three strings
would meet your requirements and is within most installers recommended
string maximum.  We have had excellent results with the VRLA
batteries although the oldest sites are floating on grid.  The
off-grid installations we have (that cycle daily) are newer so we have
less data.<br><br>
Good luck.<br><br>
William Miller<br><br>
<br>
At 08:45 PM 3/5/2009, you wrote:<br>
</font><blockquote type=cite class=cite cite><font face="arial" size=2>Hi
wrenches,<br>
I am looking for a quality battery to use in the 700-900 amp hour
range.  Anyone have any suggestions as to a good product in this
range?<br>
 <br>
Jeff Blick</font></blockquote></body>