<DIV><SPAN class=200080011-29122008><FONT face=Arial color=#0000ff size=2>I 
would first isolate your system. turn off all loads on the inverter, & 
REPOLE. check the AC input AT the inverter, checking ALL AC input connections, 
pull on the wires , make sure they are tight. Ck the AC voltage at the 
generator then at the inverter. </FONT></SPAN></DIV>
<DIV><SPAN class=200080011-29122008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=200080011-29122008><FONT face=Arial color=#0000ff size=2>Is it 
possible to run a separate wire from the gen to the inverter? sometime the 
conduit fills w/ water or  mice have chewed wires ect, Ck the temp 
sensor & remove it during testing.</FONT></SPAN></DIV>
<DIV><SPAN class=200080011-29122008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=200080011-29122008><FONT face=Arial color=#0000ff size=2>With 
the E panel their is an outlet plug in your heat gun , loading the 
generator, still have fluctuating voltages?If the batteries are low I 
would,  while watching the AC input voltage & Hzs, lower the charge 
rate to the batteries & watch these readings. Stabilize at a lower 
current?</FONT></SPAN></DIV>
<DIV><SPAN class=200080011-29122008><FONT face=Arial color=#0000ff size=2>Do you 
have a small portable gen that you can being? try that. </FONT></SPAN></DIV>
<DIV><SPAN class=200080011-29122008><FONT face=Arial color=#0000ff size=2>All 
else fails you have brought the other inverter w/ you I sometimes find it less 
time consuming to swap inverters to check, then boards. </FONT></SPAN></DIV>
<DIV><SPAN class=200080011-29122008><FONT face=Arial color=#0000ff size=2>I have 
replaced quite a few boards & yes there have been times that the AC 
board was faulty & the generator never connected. </FONT></SPAN></DIV>
<DIV><SPAN class=200080011-29122008><FONT face=Arial color=#0000ff size=2>OB is 
quite good sending boards I would REPLACE ALL if they will send them to you, AC, 
DC, & Control, If it is remote & you don't want to go back & 
forth wait until you get the boards.</FONT></SPAN></DIV>
<DIV><SPAN class=200080011-29122008><FONT face=Arial color=#0000ff size=2>As 
posted below, you have looked at most of these things I have suggested but the 
inverters,usually can w/stand a quick short,shutting the inverter down. 
</FONT></SPAN></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV></DIV>
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT 
  face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> 
  re-wrenches-bounces@lists.re-wrenches.org 
  [mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>R 
  Young<BR><B>Sent:</B> Sunday, December 28, 2008 8:51 PM<BR><B>To:</B> 
  RE-wrenches<BR><B>Subject:</B> [RE-wrenches] Outback VFX input voltage 
  cycling<BR><BR></FONT></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>This thread seems to have died ... somehow it got mixed in with the 
  "strings of different orientation" thread. If anyone has further input I would 
  very much appreciate it as I have to schedule a long trip to remedy this and 
  want to have as much ammunition as possible. Again, to restate the 
  problem:</FONT></DIV>
  <DIV style="MARGIN: 0px"><BR></DIV>
  <DIV style="MARGIN: 0px">
  <BLOCKQUOTE type="cite">
    <DIV style="MARGIN: 0px">an Outback VFX3524 inverter installed on an E-panel 
    in a remote off-grid location. Voltage at the inverter input terminals is 
    fluctuating between 110 & 140+ volts continuously. AC in will not 
    connect so batteries can't charge. Output voltage measured at the inverter 
    output terminals is steady at 122v.  When all household loads are 
    turned off the input terminal voltage stabilizes but AC In still does not 
    connect.</DIV>
    <DIV style="MIN-HEIGHT: 14px; MARGIN: 0px"><BR></DIV>
    <DIV style="MARGIN: 0px">Generator does not seem to be at fault as output 
    measured at the gen. is stable even under load. System was working for about 
    1 1/2 years but under new ownership has been badly monitored and batteries 
    have become totally discharged.</DIV>
    <DIV style="MIN-HEIGHT: 14px; MARGIN: 0px"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>I'm trying to determine if this is a circuit board problem so I can 
    perform a rescue mission by pulling some boards from an in-stock inverter, 
    Outback tech support are on holidays. Anyone had a similar 
    problem? <SPAN class=Apple-tab-span 
    style="WHITE-SPACE: pre"></SPAN></FONT></DIV></BLOCKQUOTE></DIV>
  <DIV style="MARGIN: 0px"><BR></DIV>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>Mick,</FONT></DIV>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>referring to</FONT></DIV><BR>
  <BLOCKQUOTE type="cite">
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>there's not an auto-idle switch on that genset which may have 
    accidentally been set for auto, is there?</FONT></DIV><BR></BLOCKQUOTE>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>His generator was actually running in idle mode, operating the 
  household loads when I got there and the first thing I discovered was that the 
  voltage was ~90 volts coming in to the inverter. I manually switched the 
  generator to full speed and then checked the voltage again, that is where I 
  found the rapid fluctuations occurring at the inverter.</FONT></DIV>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>Ron</FONT></DIV>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>On 27-Dec-08, at 1:23 PM, mick abraham wrote:</FONT></DIV>
  <DIV 
style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV><BR>
  <BLOCKQUOTE type="cite">
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>Ron wrote: "The owner told me...that someone had wired a switch 
    incorrectly</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>and when he turned it on the system "shut down". He then re-wired it 
    and</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>everything appeared ok but I'm wondering if this fried a 
    board."</FONT></DIV>
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>Mick replies: I've seen several times with Outback and other brands 
    (going as</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>far back as the Trace SW) where the inverter responds to an 
    accidental short</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>circuit in the household wiring by shutting itself off quicker than a 
    circuit</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>breaker can open. I'll bet that is what your customer 
    experienced...possibly</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>due to a nicked hot wire in that new switch box shorting out to 
    ground.</FONT></DIV>
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>I suspect that (part of your customer's report) is completely 
    unrelated to</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>your present problem scenario. If it was my headache I would beg, 
    borrow,</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>or...rent a second generator to insert temporarily instead of the 
    Honda 3800.</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>That's the most conclusive way to determine fault or no-fault on the 
    generator.</FONT></DIV>
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>Sometimes a genset will operate non-inverter loads OK and will 
    exhibit normal</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>looking voltage etc. but there still could be transients or spikes 
    which</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>render this input AC power unacceptable to the 
    inverter/charger.</FONT></DIV>
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>Thinking...there's not an auto-idle switch on that genset which may 
    have</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>accidentally been set for auto, is there?</FONT></DIV>
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>Mick Abraham, Proprietor</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>www.abrahamsolar.com</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>Voice: 970-731-4675</FONT></DIV></BLOCKQUOTE><BR>
  <DIV style="MARGIN: 0px">
  <BLOCKQUOTE type="cite">
    <BLOCKQUOTE type="cite">
      <DIV style="MARGIN: 0px">Hi Mick & Jay,</DIV>
      <DIV style="MARGIN: 0px">I disconnected the gen. line to the inverter and 
      tested the output and got steady voltage. I then re-connected the inverter 
      and tested the gen. output from a different outlet and got steady voltage, 
      both around 122v. So I've ruled out the generator. It was my first 
      suspicion.</DIV>
      <DIV style="MIN-HEIGHT: 14px; MARGIN: 0px"><BR></DIV>
      <DIV style="MARGIN: 0px">I have also noticed that when the household loads 
      are off the inverter output appears stable, doesn't fluctuate except about 
      every 20 seconds inverter audibly, the voltage drops from around 120 to 
      110 then resumes - as if the input was momentarily dropped.</DIV>
      <DIV style="MIN-HEIGHT: 14px; MARGIN: 0px"><BR></DIV>
      <DIV style="MARGIN: 0px">Darryl,</DIV>
      <DIV style="MARGIN: 0px">I did play with the AC charge current lowering it 
      to around 5 aac but it didn't seem to make a difference. The owner told 
      me, as an afterthought that someone had wired a switch incorrectly and 
      when he turned it on the system "shut down". He then re-wired it and 
      everything appeared ok but I'm wondering if this fried a board. I know 
      there is an ac control board in there ... could this be it?</DIV>
      <DIV style="MIN-HEIGHT: 14px; MARGIN: 0px"><BR></DIV>
      <DIV style="MARGIN: 0px">BTW, it's a very small generator, Honda 
      3800.</DIV></BLOCKQUOTE></BLOCKQUOTE></DIV>
  <DIV style="MIN-HEIGHT: 14px; MARGIN: 0px"><BR></DIV>
  <DIV style="MARGIN: 0px">Ron</DIV>
  <DIV><BR></DIV>
  <BLOCKQUOTE type="cite">
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>_______________________________________________</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>List sponsored by Home Power magazine</FONT></DIV>
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>List Address: <A 
    href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A></FONT></DIV>
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>Options & settings:</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4><A 
    href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A></FONT></DIV>
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>List-Archive: <A 
    href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A></FONT></DIV>
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>List rules & etiquette:</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>www.re-wrenches.org/etiquette.htm</FONT></DIV>
    <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>Check out participant bios:</FONT></DIV>
    <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
    size=4>www.members.re-wrenches.org</FONT></DIV>
    <DIV 
    style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV><BR></BLOCKQUOTE>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>_______________________________________________</FONT></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>List sponsored by Home Power magazine</FONT></DIV>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>List Address: <A 
  href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A></FONT></DIV>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>Options & settings:</FONT></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4><A 
  href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A></FONT></DIV>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>List-Archive: <A 
  href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A></FONT></DIV>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>List rules & etiquette:</FONT></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>www.re-wrenches.org/etiquette.htm</FONT></DIV>
  <DIV style="MIN-HEIGHT: 17px; MARGIN: 0px; FONT: 14px Helvetica"><BR></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>Check out participant bios:</FONT></DIV>
  <DIV style="MARGIN: 0px"><FONT style="FONT: 14px Helvetica" face=Helvetica 
  size=4>www.members.re-wrenches.org</FONT></DIV>