My favorite is the Sharp 175 for off-grid and solar pumping
applications; a sturdy, well built and consistent module for most
applications. You can even get them fairly often!<br>
<br>
Matt T<br>
<br>
Kirpal Khalsa wrote:
<blockquote
 cite="mide925cf120812101333y4d5f9d41j1956dcaf1d948fdc@mail.gmail.com"
 type="cite">Allen..Greetings....yes indeed it is an issue. we have
been addressing with multiple charge controllers per system. we don't
fight the current (not electrical).  In the future the way i see it-
the electronics will be more flexible and be able to handle the larger
variety of string voltages.  For example the long long long awaited
apollo solar t100 which will allow voltages to exceed the 150V limit we
have had for a long time.  They have apparently even lined up some
breakers which will work with these greater voltages.  3 modules in a
series will no longer be a maximum.  I understand midnite solar also
has a charge controller which will allow the 150V max to go by the way
side.  We are trying to be flexible as modules become less standard and
hope that the electronics will allow us to address thesee challanges as
time goes by.<br>
  <br>
One thing that we would love to see is more large wattage modules with
j boxes rather than pre-wired MC cables.  In many of our off grid
systems the array is located in readily accesible locations and
crafting a fence or sticking the array over 8 feet of the ground is a
big hassle/extra expense.  This has proven to be a bigger concern for
us rahter than the voltage variety.  If you know of any 72 cell or for
that matter 60 cell modules  which allow flex conduit between j boxes
we would love some info.......<br>
  <br>
  <br>
-- <br>
Sunny Regards,<br>
Kirpal Khalsa<br>
NABCEP Certified Solar PV Installer<br>
Renewable Energy Systems LLC<br>
  <br>
  <br>
  <div class="gmail_quote">On Wed, Dec 10, 2008 at 12:16 PM, Allan
Sindelar <span dir="ltr"><<a
 href="mailto:allan@positiveenergysolar.com">allan@positiveenergysolar.com</a>></span>
wrote:<br>
  <blockquote class="gmail_quote"
 style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
    <div>
    <p><font face="Times New Roman">Wrenches,</font>
    <br>
    <font face="Times New Roman">Here's an issue I haven't seen
directly addressed, and I would like to know what the rest of you are
doing.</font>
    <br>
    <font face="Times New Roman">It's getting harder to get 24V nominal
modules. Because the bulk of industry growth is high-voltage grid-tied
applications, modules no longer have to be a standard voltage. Just
pick the number of modules to best fit the chosen inverter's string
voltage range.</font></p>
    <p><font face="Times New Roman">But for off-grid, the odd cell
counts and resulting "nontraditional" DC input voltages challenge the
traditional rules of off-grid design. I may be fighting a losing battle
here, as the industry changes so rapidly and fundamentally. I have been
trying to stay with 72-cell modules for offgrid, as this most readily
combines with existing systems with 36-cell modules (12V) and 72-cell
modules (24V). </font></p>
    <p><font face="Times New Roman">For example, I will use the new
Canadian Solar 170-200W modules. They are 60-cell modules, with a Vmppt
of around 28 volts - too low to charge 24V batteries with a standard
charge controller. We can use them in any new systems with an MX60 or
similar voltage-converting MPPT controller. Two or three in series
would charge a 24V battery; 3 in series would charge 48V. Four in
series would violate Code, as low-temp voltage would easily exceed
150V. </font></p>
    <p><font face="Times New Roman">Unless 60-cell modules remain a
standard in the future, any future array additions would have to be on
their own charge controller, in order to match a different I-V curve
and MPP voltages into the same battery bank. Is this prohibitive? No,
it just runs counter to the longstanding standards of off-grid design
that allow modules to be added in the future: these modules will not
add well to existing systems, and will not easily allow additional
dissimilar modules to be added later. </font></p>
    <p><font face="Times New Roman">I had this same objection to using
Day4 modules, although they were better at 16Vnom. Three made up a
standard 48V array, so strings could be combined with two-module
strings of similar 24Vnom modules.</font></p>
    <p><font face="Times New Roman">Who else is trying to stay with 24V
modules? Anyone still using 12V modules in off-grid (residential-scale,
not little apps) designs? Who has a crystal ball and knows what modules
will be like in 20 years, or even two years? Wat are the rest of you
doing?</font></p>
    <p><font face="Times New Roman">Thanks, as usual.</font>
    <br>
    <font face="Times New Roman">Allan</font>
    <br>
    <font color="#888888"><font face="g">Allan Sindelar</font>
    <br>
    <a href="mailto:allan@positiveenergysolar.com" target="_blank"><u><font
 color="#0000ff" face="g" size="2">allan_(at)_positiveenergysolar.com</font></u></a>
    <br>
    <font face="g" size="2">NABCEP certified solar PV installer</font>
    <br>
    <font face="g" size="2">Positive Energy, Inc.</font>
    <br>
    <font face="g" size="2">3225A Richards Lane</font>
    <br>
    <font face="g" size="2">Santa Fe NM 87507</font>
    <br>
    <font face="g" size="2">505 424-1112</font>
    </font></p>
    </div>
  </blockquote>
  </div>
  <br>
  <br clear="all">
  <br>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

  </pre>
  <pre wrap="">
<hr size="4" width="90%">

Internal Virus Database is out of date.
Checked by AVG - <a class="moz-txt-link-freetext" href="http://www.avg.com">http://www.avg.com</a> 
Version: 8.0.176 / Virus Database: 270.9.15/1833 - Release Date: 12/5/2008 7:08 PM

  </pre>
</blockquote>
</body>
</html>