I'm dredging up this subject again (previous postings 6/08) with a simple question that doesn't seem to have been answered:<BR>
<BR>
Is there any issue connecting a batteryless grid-tie PV system to the load side of a panel that is backed-up by a generator on an automatic transfer switch, when the grid is down and the generator running?<BR>
<BR>
In this case the PV is 5.7kW, the inverter an SMA 6000, the generator unknown size/type, but propane, automatic start, and backing up the entire main panel.<BR>
<BR>
SMA tech support first said it's OK, then that the generator will blow up. I can imagine, if the inverter tries to sync with the inverter, that the voltage could rise, causing the inverter to disconnect, wait 5 minutes, repeat. Is there anything nasty that could happen? <BR>
<BR>
Thanks,<BR>
-Kelly<BR>
<BR>
<BR>
Kelly Keilwitz, P.E.<BR>
Whidbey Sun & Wind, LLC<BR>
Renewable Energy Systems<BR>
NABCEP Certified PV Installer<BR>
987 Wanamaker Rd, <BR>
Coupeville, WA 98239 <BR>
PH & FAX 360-678-7131<BR>
<FONT COLOR="#0000FF"><U><a href="sunwind@whidbeysunwind.com">sunwind@whidbeysunwind.com</a><BR>
</U></FONT> <BR>
</SPAN></FONT><SPAN STYLE='font-size:12pt'><FONT FACE="Verdana, Helvetica, Arial"><BR>
</FONT><FONT FACE="Monaco, Courier New"><BR>
</FONT></SPAN><FONT FACE="Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT SIZE="1"><FONT FACE="Verdana, Helvetica, Arial"><SPAN STYLE='font-size:9pt'> <BR>
</SPAN></FONT></FONT><FONT FACE="Verdana, Helvetica, Arial"><SPAN STYLE='font-size:12pt'><BR>
</SPAN></FONT>
</BODY>
</HTML>