<DIV><SPAN class=531414617-03112008><FONT face=Arial color=#0000ff size=2>Mario,
what you are looking in any gen set application is the fuel solenoid valve.
</FONT></SPAN></DIV>
<DIV><SPAN class=531414617-03112008><FONT face=Arial color=#0000ff size=2>On the
KOHLER 8/12 RES units, if you are facing the open door/run/auto switch,the right
side of the enclosure is removed.END of the unit. Inside this space
top left corner is our propane inlet. you will see, depending on your fuel
Nat/Propane wires labeled "70A & 70B" plus " N4" These are 12 Volt
& this is where you piggy back your source for your GSM. If the unit fails
to start the controller in the gen set will disable the voltage to these
solenoids shutting the GSM & the gen set down. BE aware that some of the old
RES units we needed to install a receptacle for the 120/12 volt battery
charger.The new ones have the receptacle BUT it needs to be wired into the
output circuit of the generator.There is NOT a charging circuit on these units,
prolong operation w/o the aid of a battery charging source will cause a shut
down.</FONT></SPAN></DIV>
<DIV><SPAN class=531414617-03112008><FONT face=Arial color=#0000ff
size=2>Additional Information can be found at the downloads site @ <A
href="http://www.kohlerpower.com">www.kohlerpower.com</A>
bulletin TP-6514</FONT></SPAN></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
<DIV></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT
face=Tahoma size=2>-----Original Message-----<BR><B>From:</B>
re-wrenches-bounces@lists.re-wrenches.org
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of
</B>Mario@bestpowersolar.net<BR><B>Sent:</B> Monday, November 03, 2008 12:03
PM<BR><B>To:</B> RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] Magnum AGS
with Kohler RES 8.5<BR><BR></FONT></DIV>
<DIV><FONT face=Arial size=2>Tump, Dave,</FONT></DIV>
<DIV><FONT face=Arial size=2>This is very timely info for us. Could you
pass the diagrams along? </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Thanks,</FONT></DIV>
<DIV><FONT face=Arial size=2>Mario</FONT></DIV>
<DIV><FONT face=Arial size=2>Mario@bestpowersolar.net</FONT></DIV>
<BLOCKQUOTE
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
<DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
<DIV
style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B>
<A title=tump@hughes.net href="mailto:tump@hughes.net">Tump</A> </DIV>
<DIV style="FONT: 10pt arial"><B>To:</B> <A
title=re-wrenches@lists.re-wrenches.org
href="mailto:re-wrenches@lists.re-wrenches.org">'RE-wrenches'</A> </DIV>
<DIV style="FONT: 10pt arial"><B>Sent:</B> Monday, November 03, 2008 10:51
AM</DIV>
<DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] Magnum AGS
with Kohler RES 8.5</DIV>
<DIV><BR></DIV>
<DIV><SPAN class=250245016-03112008><FONT face=Arial color=#0000ff
size=2>DAVE did you get this information on Friday? let me know if you need
additional info, as I do have wire diagrams for Kohler gen sets.
TUMP</FONT></SPAN></DIV>
<BLOCKQUOTE style="MARGIN-RIGHT: 0px">
<DIV></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT
face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> <A
href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</A>
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of
</B>robert ellison<BR><B>Sent:</B> Monday, November 03, 2008 10:37
AM<BR><B>To:</B> RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] Magnum
AGS with Kohler RES 8.5<BR><BR></FONT></DIV>
<DIV>Hi Dave,</DIV>
<DIV> </DIV>
<DIV>Try the oil pressure wire, it probably is live when running but I
have seen some shut down systems that go to ground to stop, might not
work there. <BR></DIV>
<DIV>Don't give up on them yet, I expect that I know who that was at tech
and he still has some learning to do.</DIV>
<DIV>He once told me that he would not trust the voltage and amp readings
off an e meter / link 10 because he had never heard of it.</DIV>
<DIV> </DIV>
<DIV>Tony is real good. Next time you get the other fellow ask for
Tony or call back.</DIV>
<DIV>There is a wide selection of different start systems out there and it
can be real hard to get the right plans. Sometimes I think they do in
intentionally.... (the set manufacturers)</DIV>
<DIV> </DIV>
<DIV>Later,</DIV>
<DIV>Bob</DIV>
<DIV><BR> </DIV>
<DIV class=gmail_quote>On Fri, Oct 31, 2008 at 2:03 PM, David Palumbo
<SPAN dir=ltr><<A
href="mailto:dave@independentpowerllc.com">dave@independentpowerllc.com</A>></SPAN>
wrote:<BR>
<BLOCKQUOTE class=gmail_quote
style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">
<DIV text="#000000" bgcolor="#ffffff">
<DIV><FONT face=Arial color=#0000ff
size=2><SPAN>Wrenchsters,</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff
size=2><SPAN></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN>We have a new 3.4kW PV
off grid installation that includes a Magnum ME-AGS Auto Gen Start
module, Magnum ME-RC50 Remote Control, MS4448AE inverter and a Kohler
8.5 RES lp gas generator for automatic backup battery charging (16
L-16G's).</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff
size=2><SPAN></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN>We have successfully
used a Magnum AGS control Magnum with an older 3 wire start Onan
although it took some time in finding 12 volts that is only on when the
gen is running (typically the hour meter power).</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff
size=2><SPAN></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN>With the Kohler 8.5 RES
there is no hour meter or other obvious location in the generator for
12v power that is only on when the gen is running. We called Magnum
from the site only to be told that all of the information we needed
was on line. The man was still un-helpful when we told him that we were
on a remote installation with no internet access. Now I'm back at the
shop and on the web. On the Magnum web site I see a hook-up diagram
for their AGS with a Kohler RMY series generator. Nothing for a RES
series.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff
size=2><SPAN></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN>Next time we'll go back
to OutBack.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff
size=2><SPAN></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN>Any help that the
wrench community can lend on working this situation out would be
appreciated.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff
size=2><SPAN></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN>Dave
Palumbo</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN>Independent Power
LLC</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff
size=2><SPAN></SPAN></FONT> </DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px"><FONT face=Arial
color=#0000ff
size=2></FONT> </BLOCKQUOTE></DIV><BR>_______________________________________________<BR>List
sponsored by Home Power magazine<BR><BR>List Address: <A
href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options
& settings:<BR><A
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive:
<A
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
target=_blank>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List
rules & etiquette:<BR><A
href="http://www.re-wrenches.org/etiquette.htm"
target=_blank>www.re-wrenches.org/etiquette.htm</A><BR><BR>Check out
participant bios:<BR><A href="http://www.members.re-wrenches.org/"
target=_blank>www.members.re-wrenches.org</A><BR><BR><BR></BLOCKQUOTE></DIV><BR></BLOCKQUOTE>
<P>
<HR>
<P></P>_______________________________________________<BR>List sponsored by
Home Power magazine<BR><BR>List Address:
RE-wrenches@lists.re-wrenches.org<BR><BR>Options &
settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List
rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out
participant
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BLOCKQUOTE></BODY></HTML>