<DIV><FONT face=Arial size=2>Tump, Dave,</FONT></DIV>
<DIV><FONT face=Arial size=2>This is very timely info for us.  Could you 
pass the diagrams along? </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Thanks,</FONT></DIV>
<DIV><FONT face=Arial size=2>Mario</FONT></DIV>
<DIV><FONT face=Arial size=2>Mario@bestpowersolar.net</FONT></DIV>
<BLOCKQUOTE 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=tump@hughes.net href="mailto:tump@hughes.net">Tump</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">'RE-wrenches'</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Monday, November 03, 2008 10:51 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] Magnum AGS 
  with Kohler RES 8.5</DIV>
  <DIV><BR></DIV>
  <DIV><SPAN class=250245016-03112008><FONT face=Arial color=#0000ff size=2>DAVE 
  did you get this information on Friday? let me know if you need additional 
  info, as I do have wire diagrams for Kohler gen sets. TUMP</FONT></SPAN></DIV>
  <BLOCKQUOTE style="MARGIN-RIGHT: 0px">
    <DIV></DIV>
    <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT 
    face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> <A 
    href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</A> 
    [mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
    </B>robert ellison<BR><B>Sent:</B> Monday, November 03, 2008 10:37 
    AM<BR><B>To:</B> RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] Magnum AGS 
    with Kohler RES 8.5<BR><BR></FONT></DIV>
    <DIV>Hi Dave,</DIV>
    <DIV> </DIV>
    <DIV>Try the oil pressure wire, it probably is live when running but I have 
    seen some shut down systems that go to ground to stop, might not work 
    there.  <BR></DIV>
    <DIV>Don't give up on them yet, I expect that I know who that was at tech 
    and he still has some learning to do.</DIV>
    <DIV>He once told me that he would not trust the voltage and amp readings 
    off an e meter / link 10 because he had never heard of it.</DIV>
    <DIV> </DIV>
    <DIV>Tony is real good. Next time you get the other fellow ask for Tony 
    or call back.</DIV>
    <DIV>There is a wide selection of different start systems out there and it 
    can be real hard to get the right plans. Sometimes I think they do in 
    intentionally.... (the set manufacturers)</DIV>
    <DIV> </DIV>
    <DIV>Later,</DIV>
    <DIV>Bob</DIV>
    <DIV><BR> </DIV>
    <DIV class=gmail_quote>On Fri, Oct 31, 2008 at 2:03 PM, David Palumbo <SPAN 
    dir=ltr><<A 
    href="mailto:dave@independentpowerllc.com">dave@independentpowerllc.com</A>></SPAN> 
    wrote:<BR>
    <BLOCKQUOTE class=gmail_quote 
    style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">
      <DIV bgcolor="#ffffff" text="#000000">
      <DIV><FONT face=Arial color=#0000ff 
      size=2><SPAN>Wrenchsters,</SPAN></FONT></DIV>
      <DIV><FONT face=Arial color=#0000ff 
size=2><SPAN></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial color=#0000ff size=2><SPAN>We have a new 3.4kW PV 
      off grid installation that includes a Magnum ME-AGS Auto Gen Start module, 
      Magnum ME-RC50 Remote Control, MS4448AE inverter and a Kohler 8.5 RES lp 
      gas generator for automatic backup battery charging (16 
      L-16G's).</SPAN></FONT></DIV>
      <DIV><FONT face=Arial color=#0000ff 
size=2><SPAN></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial color=#0000ff size=2><SPAN>We have successfully used 
      a Magnum AGS control Magnum with an older 3 wire start Onan although it 
      took some time in finding 12 volts that is only on when the gen is running 
      (typically the hour meter power).</SPAN></FONT></DIV>
      <DIV><FONT face=Arial color=#0000ff 
size=2><SPAN></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial color=#0000ff size=2><SPAN>With the Kohler 8.5 RES 
      there is no hour meter or other obvious location in the generator for 12v 
      power that is only on when the gen is running. We called Magnum from 
      the site only to be told that all of the information we needed was on 
      line. The man was still un-helpful when we told him that we were on a 
      remote installation with no internet access. Now I'm back at the 
      shop and on the web. On the Magnum web site I see a hook-up diagram 
      for their AGS with a Kohler RMY series generator. Nothing for a RES 
      series.</SPAN></FONT></DIV>
      <DIV><FONT face=Arial color=#0000ff 
size=2><SPAN></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial color=#0000ff size=2><SPAN>Next time we'll go back 
      to OutBack.</SPAN></FONT></DIV>
      <DIV><FONT face=Arial color=#0000ff 
size=2><SPAN></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial color=#0000ff size=2><SPAN>Any help that the wrench 
      community can lend on working this situation out would be 
      appreciated.</SPAN></FONT></DIV>
      <DIV><FONT face=Arial color=#0000ff 
size=2><SPAN></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial color=#0000ff size=2><SPAN>Dave 
      Palumbo</SPAN></FONT></DIV>
      <DIV><FONT face=Arial color=#0000ff size=2><SPAN>Independent Power 
      LLC</SPAN></FONT></DIV>
      <DIV><FONT face=Arial color=#0000ff 
size=2><SPAN></SPAN></FONT> </DIV>
      <BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px"><FONT face=Arial 
        color=#0000ff 
      size=2></FONT> </BLOCKQUOTE></DIV><BR>_______________________________________________<BR>List 
      sponsored by Home Power magazine<BR><BR>List Address: <A 
      href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options 
      & settings:<BR><A 
      href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" 
      target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
      <A 
      href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" 
      target=_blank>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List 
      rules & etiquette:<BR><A 
      href="http://www.re-wrenches.org/etiquette.htm" 
      target=_blank>www.re-wrenches.org/etiquette.htm</A><BR><BR>Check out 
      participant bios:<BR><A href="http://www.members.re-wrenches.org/" 
      target=_blank>www.members.re-wrenches.org</A><BR><BR><BR></BLOCKQUOTE></DIV><BR></BLOCKQUOTE>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>