<DIV style="font-family:Arial, sans-serif; font-size:10pt;"><DIV>Thanks for all the great feedback.  This installation was more screwed up than Hogan's goat, so replacing the inverter is the least of the clients problems.  I found that there was no ground wires to any modules, no ground rod, no GFI, and it is a metal pole mounted array located in the center of a grade school playground and has made a great jungle gym.   This system passed city electrical inspection, so what else is new!</DIV>
<DIV> </DIV>
<DIV>Most likely we will be asked to totally rework and replace the inverter with a different brand after we install an approved grounding system, and yes, we will need to rewire the array for a higher voltage since this system was set up for less than 80 volts DC input.</DIV>
<DIV> </DIV>
<DIV>Thanks again to all including those who wrote off-line,</DIV>
<DIV> </DIV>
<DIV>Jeff Yago<BR></DIV><BR> <BR><HR>Netscape.  Just the Net You Need.</DIV>