 style="font-family: -moz-fixed; font-size: 13px;" lang="x-western">Mark,
<br>
Does this customer have another charging source besides a generator,
like PV  ?   That last few percent SOC
<br>
into the batteries is very inefficient of course.  If they are 
starting to charge their batteries only when the inverter cuts
<br>
out due to under-voltage cut out, it may be that they have more of a
problem than getting that last 1% into the
<br>
bank ?   Even if it's charged to anywhere ~near~ 99%, the bank is
running down pretty low (less than 50% SOC anyway)
<br>
<br>
OK, so the BMK (Magnum's battery monitor),  uses 3 criteria which must
all be met before it will give you that
<br>
last 1% State Of Charge....
<br>
<br>
1) The return Amps must go below 2% of the Amp-Hour setting for the
battery bank (settings via the remote).
<br>
<br>
2)  Battery voltage Vs. Time...  The battery voltage must remain at a
voltage for a certain amount of time.
<br>
    The lower the battery voltage, the longer this time it must remain
there. .As long as criteria 1 and 3 are met,
<br>
    say, if you were in Float (~13.5V per 12V battery), that time is
around 10 minutes.
<br>
<br>
3) The Amp-Hours IN-to the battery must be within 1% of the A-H that
came OUT.
<br>
<br>
I am assured (from Magnum) that when it reads 99% SOC it is at ~least~ 
99% SOC.
<br>
<br>
As for the bridge fault error, It may or may not be an actual problem. 
There has been (as I thought) a software fix in case it
<br>
is a nuisance message, that did plague a few of the earlier MS4448AE
units.
<br>
<br>
This all being said, I have included (below) an email I received from
Glen Darby, one of our customer service guys downstairs.
<br>
<br>
Have a day and 1/2  !
<br>
boB Gudgel
<br>
<br>
<br>
<br>
Bob,
<br>
Your question
<br>
<br>
(1) Magnum's integrated battery monitor hasn't done a 100% reset for
some
<br>
> time. It counts up to 99%, no more Is this an equipment glitch?
OR: should we fool the system into repeating the
<br>
> bulk charge to try again for the reset?
<br>
<br>
I would try setting the total amp hrs a little lower and do a reset.
<br>
<br>
2) The client reports an "Internal Bridge" fault.
<br>
<br>
This is not normal and if this fault comes back again, the customer
should call our tech
<br>
support (425-353-8833) at the time it is in a fault mode so we can
trouble shoot the unit.
<br>
The Internal Bridge fault means that the unit senses no ac output
voltage or current when
<br>
it senses voltage on the input. It shuts down to protect the fets. 
This should not be
<br>
caused by the low DCV.
<br>
<br>
Thank you
<br>
<br>
(Glen)
<br>
<br>
<br>
boB wrote:
<br>
<blockquote type="cite">mick abraham wrote:
  <br>
  <blockquote type="cite">Greetings, all~
    <br>
    <br>
If there is no Magnum employee monitoring the Wrench List, could boB
Gudgel forward this as appropriate?
    <br>
    <br>
My client has a "genset plus" system--no recharge other than his
MagnaSine
    <br>
4448AE driven by a generator. Batteries are a single string of Deka
8L-16's, a
    <br>
few months old. We're running the charger defaults: 48 amp maximum
charge
    <br>
rate, 2 hour absorption, and flooded setpoints.
    <br>
    <br>
(1) Magnum's integrated battery monitor hasn't done a 100% reset for
some
    <br>
time. It counts up to 99%, no more, according to the report from my
customer.
    <br>
I asked the customer to run the generator for longer than his normal
pattern,
    <br>
in order to force the meter to reset (and also to increase battery
SOC). The
    <br>
"AH I/O" counter ran up to about 78 amp hours above zero and the
    <br>
inverter/charger went into float for over an hour...but still we got no
reset
    <br>
on the counters.
    <br>
Is this an equipment glitch? OR: should we fool the system into
repeating the
    <br>
bulk charge to try again for the reset?
    <br>
(2) The client reports an "Internal Bridge" fault. This has happened
multiple
    <br>
times because the customer has become adept at resetting the unit per
page 36
    <br>
of the manual. The manual says nothing about "internal bridge", but
repeated
    <br>
shutdowns seem non-normal to me. I do notice something in the manual
about the
    <br>
"FET Bridge" so maybe that's where the trouble is.
    <br>
The customer has been pounding their batteries by driving the inverter
until
    <br>
it shuts down due to low battery voltage. Could that trigger the
"Internal
    <br>
Bridge" fault? It certainly triggers my cringe reflex...
    <br>
    <br>
If we can get the percentage meter back on track, that might help
reduce the
    <br>
customer's "drive until it dies" behavior. Here's hoping...
    <br>
    <br>
Thankx,
    <br>
    <br>
Mick Abraham, Proprietor
    <br>
    <a class="moz-txt-link-abbreviated"
 href="http://www.abrahamsolar.com">www.abrahamsolar.com</a>
    <br>
Voice: 970-731-4675
    <br>
  </blockquote>
  <br>
No problem, Mark.   Your info is being forwarded to the Magnum
Engineering department now and I will follow up
  <br>
on this when I get in tomorrow morning.  The 99% (BMK) issue is
familiar but I can't remember off hand exactly what the
  <br>
solution is.  I believe  the internal bridge fault (inverter), was on
earlier units and has a software fix  as I remember.
  <br>
You should get more info hopefully tomorrow.
  <br>
  <br>
Thanks,
  <br>
boB