<DIV><SPAN class=359494905-10092008>Jeff,</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>Re remote starting, we have had experience 
with these generators as being two-wire and easy to control:</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>    -all Kohler LP from the 
old 6.5RMY through 20RY</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>    -Onan RS20000 - I 
understand the new units are 2-wire like Kohler. This one was.</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>    -Coleman 10kW with Honda 
engine.</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>All required two wires only and no 
additional hardware.</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>Allan</SPAN></DIV>
<DIV><SPAN class=359494905-10092008></SPAN> </DIV>
<DIV></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT face=Tahoma 
size=2>-----Original Message-----<BR><B>From:</B> 
re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>Jeff 
Yago<BR><B>Sent:</B> Wednesday, September 03, 2008 9:43 AM<BR><B>To:</B> 
RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] Remote generator 
start<BR><BR></FONT></DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: Arial, sans-serif">
<DIV>I know this subject has come up from time to time in small pieces, but 
would like a collective set of answers.  As you know, some generators are 
very easy to remote start from an inverter using only a simple relay and 2-wire 
connection.  Make the contact and the generator starts and runs, break the 
contact and it stops.  The Kohler line of generators have this start and 
stop control and was easy to connect to the spare relay in the old Trace 
SW40 inverter and the newer Outback inverters.</DIV>
<DIV> </DIV>
<DIV>What generators in the 8 to 15 kW range have you found easy to remote 
start from an inverter, and which models or brands were a nightmare?  
</DIV>
<DIV> </DIV>
<DIV>What other hardware or controls were required to get it to 
work?   </DIV>
<DIV> </DIV>
<DIV>How many control wires were required out to the generator?</DIV>
<DIV> </DIV></DIV></BODY></HTML>