Marco, when I refer to ‘grounding
the array’ I am referring to PV electrical grounding. This is the grounding
of the + or – PV conductor. In most (99.9%) US installations the negative
conductor this is grounded at/within the inverter. This electrical ground may be
made at only one location. This is done to create a ground loop path in the
event of an electrical earth ground fault in the array system. The intent is to
‘collapse’ the array so that high voltage will not be on the array
frame or electrical chassis and be a threat to personnel. It also allows for
detection of ground fault current by the inverter (or other means of current
sensing) to disable the inverter and annunciate the fault. This does not
protect against continuous ground current flow, up to the Isc
of the entire array, caused by multiple ground faults in the array. There are
more effective means of ground fault protection using voltage differential measurement
techniques, which do not require PV array grounding, but the NEC won’t
allow it. There is much debate over this subject, as the
I was not referring to the chassis or
safety grounding of the PV array frame, structure, conduit, enclosure chassis,
etc. This is entirely different than the electrical grounding. Yes, you must
ground the PV panel frames to earth ground at multiple locations. Safety grounding
is covered in various places in NEC and, in general, may be grounded all over
the array field at multiple locations (something like every 6 feet). My only
recommendation with safety grounding is to bond all earth ground stakes
together and bond them to the primary point of electrical earth ground. This is
usually near the building distribution transformer.
Hope this helps and doesn’t cause
more confusion.
____________________________________________
Kent Sheldon
Manager, Industrial Power
Systems
SMA America
925 513 8813
Brentwood Office (Primary)
530 273 4848 Grass Valley
Office
-----Original Message-----
From:
Sent: Saturday, January 12, 2002 4:14 PM
To: RE-wrenches@topica.com
Subject: RE: grounding array/sunny
boy [RE-wrenches]
Kent,
In my effort to get things "perfectly clear"
(as Richard Nixon once said while trying to explain his involvement with the
Watergate scandal), when you say that you cannot ground the PV array anywhere
else, you're not saying to not bond the module frames back to earth ground,
right? Or to put it an another way, modules which have metal frames need
to have those frames bonded/grounded to earth regardless of the type of
inverter or system design, right?
marco
ProVision Technologies
Hilo (hello!), Hawai'i nei
- - - - To send a message: RE-wrenches@topica.com Archive of previous messages: http://www.topica.com/lists/RE-wrenches/ List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm Check out participant bios: www.mrsharkey.com/wrenches/index.html Hosted by Home Power magazine Moderator: michael.welch@homepower.com
==^================================================================ This email was sent to: michael.welch@homepower.com EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9 Or send an email to: RE-wrenches-unsubscribe@topica.com T O P I C A -- Register now to manage your mail! http://www.topica.com/partner/tag02/register ==^================================================================