Travis,
Not knowing William Miller's approach, I
think Phil has hit it well, once you add that relay on the signal
circuit. I like relays--simple, reliable, can be a long distance away,
and lets DC control AC for phantom load mgt. Anyway, put the relay on
the ATS' genstart circuit, then design your controls on the coil circuit of
the relay. Use combinations of series and parallel logic to (for
example): let one of the Trace's auxiliary voltage relays allow gen start
based on voltage, OR the E-meter's LLO to base on % SOC, AND/OR
a load-based switch start on the client's gennie-only loads (turning on
the device also sends a start signal to this relay to start gennie), OR an
exercise timer (Trace or separate). You can add a Todd TS30 or TS50 to one or
more AC gennie loads to provide time-delay and multiple load switching (MORE
relays! Yummy!) You can even sequence relays, so that big load A both starts
the gennie AND disconnects AC to the inverter, if the total load is too big,
but smaller load B allows BU charging as well.
Generic, but I hope this
helps.
Allan
----- Original Message -----
Sent: Monday, February 05, 2001 12:11
PM
Subject: Re: Generator Control- A
Doozie [RE-wrenches]
How about this:
Grid power goes through ATS to the main load center, which
has a 2 pole 60A breaker sending power to AC1. Inverters feed a
critical load panel. Generator's start circuit is removed from the ATS
and wired to the inverters.
Power outages transfer ATS to emergency power position,
but cannot start generator. Main load center is not powered, but
the inverters feed the critical loads. At a programmed voltage or
amperage point, the inverters start the generator, which feeds thru the ATS
to the main load panel and therefore AC1 for charging.
Possible problems: too much load on main panel to
leave power for charging.
Also, does that ATS sense generator input and executes a
time-delay before latching, or does it latch after a time delay from
losing grid power? One allows the generator to warm up, the other
doesn't. Also, are your inverters in sell mode? could we have
the inverters attempting to "sell back" to the generator, and what
would that cause?
The inverter should be able to be connected in
parallel with the ATS, if you wanted the ATS to govern the excersize cycle,
but the inverters can do the same thing with more flexibility.
BTW, why a 12 volt system for a dual SW? The thought
of that much current flowing makes me wince. Hope all the wire near
your shunt is rated 90 degree Celcius or better.
----- Original Message -----
Sent: Monday, February 05, 2001 9:55
AM
Subject: Generator Control- A Doozie
[RE-wrenches]
I have a customer who already had a 22 kW
kohler controlled by a automatic transfer switch. We added solar and
a dual SW inverter system to the house. Due to the size of the
existing generator and existing house wiring
configuration I can't run the generator into AC2 on the
SW's. There are loads on the main panel that he would like to run
still that shoudn't be ran of the inverters.
I am trying to figure out a way to prevent
the generator from running when the grid is down and the batteries are
charged while allowing the generator to start when (as) the
batteries become depleted. The customer is adamant about this being
automatic.
- - - - - - -
To send a message:
RE-wrenches@topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe@topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch@homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
- - - - - - -
To send a message:
RE-wrenches@topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe@topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch@homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01