Hi All,

Twice in a week must be some sort of record for me but I think the question about surge capability and who has the most muscle is being oversimplified here. The "raw numbers" posted here don't take into account the AC voltage at the time the surge currents are being produced. Some machines, such as the SW5548 have much tighter AC voltage windows and will not allow the inverter output voltage to sag but a few volts. Others such as the notable 3624 will produce huge amounts of raw current with pretty wide voltage drops on startup. In a very real way, the quality of power being delivered when the inverter is "surging" is a design choice.

I got some help from our Engineering department and they produced the following explanation and table

Here are 5 second surge ratings with the AC output voltage measured at the end of the 5 second period. The load used was resistive (light bulbs) and the load was applied and quickly ramped (in about 1 second) from zero to the rated power via a large variac. The watts are "real" watts, measured with a Fluke 41B and a Power Tracer metering system. The battery bank consisted of sixteen L16 batteries with short 4/0 AWG battery cables. Actual field performance may be reduced by tripping of the battery breaker or blowing of the battery fuse depending upon its ratings and time delay characteristics.

MODEL     RATED POWER     VOLTAGE         OUTPUT POWER @ OUTPUT VAC

DR1512     1500 watts             12 VDC                 2400 watts @ 105 vac

DR1524     1500 watts            24 VDC                 3600 watts @ 111 vac

DR2412     2400 watts             12 VDC                 4200 watts @ 104 vac

DR2424     2400 watts             24 VDC                 6200 watts @ 109 vac

DR3624     3600 watts             24 VDC                 7500 watts @ 103 vac

SW4024    4000 watts             24 VDC                8000 watts @ 113 vac

SW4048    4000 watts             48 VDC                8800 watts @ 115 vac

SW5548    5500 watts             48 VDC                 9500 watts @ 117 vac

This is very different than the normal 1 ms / 100 ms surge rating of amps and is better for understanding the ability of the different inverters to operate multiple AC loads. This does not represent motor start capabilities as this issue is more complicated. I hope that this clarifies the subject of inverter surge behavior some.

Best regards,

Ezra Auerbach

Xantrex Technology Inc.

- - - - - - -
To send a message:
 RE-wrenches@topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe@topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch@homepower.com
____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Your Favorite Topics
Manage your email with MyTopica: http://www.topica.com/partner/tag01/my