I am not trying to be difficult here but my source just returned from Traces repair workshop (so that they can be authourized repair). What Charlie told me that so amazed him was the huge differences between the different models and that the largest surge ( he was told by the engineers in the testing division?) was not that 48v versions listed below.
I was able to look at testing numbers for those models that were what I posted the other day. Charlie also mentioned that the surge for the 48v models is only like 1 sec max ( at the 78 amps) vs 1 minute for the 4024 versions.
Now I am back to not knowing anything. I don't know which information actually is applicable in the field or in the testing lab?
From the real standpoint, rarely have I seen a SW inverter shut down from overload except for low battery. But still would be nice toknow what numbers are what??
Thanks for all the help Ezra, hopefully we can get to the bottom of this.
Jay
Peltz Power
"Ezra Auerbach, Trace Engineering" wrote:
Hi All,Twice in a week must be some sort of record for me but I think the question about surge capability and who has the most muscle is being oversimplified here. The "raw numbers" posted here don't take into account the AC voltage at the time the surge currents are being produced. Some machines, such as the SW5548 have much tighter AC voltage windows and will not allow the inverter output voltage to sag but a few volts. Others such as the notable 3624 will produce huge amounts of raw current with pretty wide voltage drops on startup. In a very real way, the quality of power being delivered when the inverter is "surging" is a design choice.
I got some help from our Engineering department and they produced the following explanation and table
Here are 5 second surge ratings with the AC output voltage measured at the end of the 5 second period. The load used was resistive (light bulbs) and the load was applied and quickly ramped (in about 1 second) from zero to the rated power via a large variac. The watts are "real" watts, measured with a Fluke 41B and a Power Tracer metering system. The battery bank consisted of sixteen L16 batteries with short 4/0 AWG battery cables. Actual field performance may be reduced by tripping of the battery breaker or blowing of the battery fuse depending upon its ratings and time delay characteristics.
MODEL RATED POWER VOLTAGE OUTPUT POWER @ OUTPUT VAC Best regards,DR1512 1500 watts 12 VDC 2400 watts @ 105 vac
DR1524 1500 watts 24 VDC 3600 watts @ 111 vac
DR2412 2400 watts 12 VDC 4200 watts @ 104 vac
DR2424 2400 watts 24 VDC 6200 watts @ 109 vac
DR3624 3600 watts 24 VDC 7500 watts @ 103 vac
SW4024 4000 watts 24 VDC 8000 watts @ 113 vac
SW4048 4000 watts 48 VDC 8800 watts @ 115 vac
SW5548 5500 watts 48 VDC 9500 watts @ 117 vac
This is very different than the normal 1 ms / 100 ms surge rating of amps and is better for understanding the ability of the different inverters to operate multiple AC loads. This does not represent motor start capabilities as this issue is more complicated. I hope that this clarifies the subject of inverter surge behavior some.
Ezra Auerbach
Xantrex Technology Inc.
- - - - - - - To send a message: RE-wrenches@topica.com The archive of previous messages: http://www.topica.com/lists/RE-wrenches/ To unsubscribe send a message to: RE-wrenches-unsubscribe@topica.com To check out the other RE-Wrench participants: www.mrsharkey.com/wrenches/index.html Hosted by Home Power magazine: www.homepower.com For info contact list moderator by email: michael.welch@homepower.com____________________________________________________________ T O P I C A -- Learn More. Surf Less. Newsletters, Tips and Discussions on Your Favorite Topics Manage your email with MyTopica: http://www.topica.com/partner/tag01/my
- - - - - - - To send a message: RE-wrenches@topica.com The archive of previous messages: http://www.topica.com/lists/RE-wrenches/ To unsubscribe send a message to: RE-wrenches-unsubscribe@topica.com To check out the other RE-Wrench participants: www.mrsharkey.com/wrenches/index.html Hosted by Home Power magazine: www.homepower.com For info contact list moderator by email: michael.welch@homepower.com