Hey
Wrenches,
There has been a change in
the wording of the 99 Code that might make array wiring easier. The use of
a combiner box might become a rare thing on domestic PV systems. Let me
know if you think this is correct.
In the old code it appeared that every
series set of modules needed to have its output run directly to an
overcurrent device in a combiner box. Connections could not be made in
another module's junction box, if removal of that module would disrupt the
"grounded conductor" of another set.
This is how it has often been interpreted in Colorado anyway. With
this method, a rack of 8 modules wired for 24 volts requires four flexible
conduit "whips" coming down to a combiner box with four fuses. There are
often positive and negative busbars to which the system conductors are
connected. Below is the old wording.
*************************************************************************************************
690-4(c) 1996 NEC
(c) Module Connection Arrangement. The connections to a module or
panel shall be so arranged that removal of a module or panel from a photovoltaic
source circuit does not interrupt a grounded conductor to another photovoltaic
source circuit.
************************************************************************************************
The new code goes into detail about the meaning of
"source circuit." It now appears that a source circuit is any
configuration of modules rated at 50 volts or less, terminating in a single over
current device. Here is the section.
**********************************************************************************************
690-4(c) 1999
NEC
(c) Module Connection Arrangement. The connections to a module or panel
shall be arranged so that removal of a module or panel from a photovoltaic
source circuit does not interrupt a grounded conductor to another photovoltaic
source circuit. Sets of modules interconnected as systems rated at 50 volts or
less, with or without blocking diodes, and having a single overcurrent device
shall be considered as a single-source circuit. Supplementary overcurrent
devices used for the exclusive protection of the photovoltaic modules are not
considered as overcurrent devices for the purpose of this section.
*******************************************************************************************
The first sentence of the new code reads exactly like the old. To
simplify the changes, we can eliminate it. The changed part has
a lot of modifying wording. Although necessary to consider, we can
eliminate the modifiers for present purposes. The reduced statement
boils down to:
Sets of modules interconnected as systems rated at 50 volts or less having
a single overcurrent device shall be considered as a single-source
circuit.
This would seem to imply that a rack of 8 modules wired in a 24
volt series-parallel configuration is a single source circuit. It would
therefore need only one whip going to a disconnect, rather than 4 whips
connecting to a combiner box.
The series sets apparently may be paralleled in the module junction
boxes now. If true, this will not only save hundreds of dollars in
materials and labor on large systems, it will also make arrays look a lot
cleaner.
Here is an example of how an array might be
designed with the new code.
Eight Siemens SP 75s wired in series-parallel for
24 volts, have a short circuit rating of 19.2 amps (4.8 X 4) . Multiply
that times 1.25 twice (to comply with code) and you get 30 amps. A pair of
number 10 THWN-2 wires should satisfy any inspector. (* Note: The
rating of THWN-2 comes on many THHN
conductors).
So two #10 AWG wires can be used instead of
eight. One conduit is needed instead of four. One overcurrent device
is needed instead of four. The wiring can be run directly to a fused
disconnect, rather than to a combiner box first. A 16 module, 24 volt
array can have two whips run to a 2 pole fused disconnect.
Due to the language, it looks hopeful that this
rule will also apply to 48 volt systems. The code now seems to say that
photovoltaic source circuits are "Sets of modules interconnected as systems
rated at 50 volts or less." The word "rated" seems to imply nominal
voltage rather than the actual measured, operating voltage.
Wrenches, let us know if we are on
track.
Drake
Chamberlin
Don
Wallingford