[RE-wrenches] Relay Drivers

Kent kent at coveoregon.com
Wed Jul 22 18:51:40 PDT 2026


Drake,

The Morningstar relay driver doesn't output voltage; it can sink current 
or measure voltage. Normally the outputs are wired to the same source 
that powers the relay driver - it is the power source that is putting 
out voltage. It shouldn't be a problem to run a 12-volt relay from a 
separate 12-volt source (or 12 volts derived from the 48-volt source) as 
long as the ground of the separate source is common with the relay 
driver ground. Simply add a 48V to 12V converter to the project and you 
can operate one to four 12-volt relays, or a mix with some being 12 and 
others being 48 volts.

Kent Osterberg
Blue Mountain Solar


On 7/21/2026 6:35 AM, Drake Chamberlin via RE-wrenches wrote:
> Hello,
> The Morningstar relay driver is a great device. It can measure 48VDC 
> nominal and operate relays based on the measured voltage. The problem 
> is that, if it is measuring 48VDC nominal, it outputs the same.
> Is there anything besides a charge controller that can measure 48 VDC 
> nominal and put out a small 12VDC current? The 12VDC output of an 
> Outback or Midnite charge control is perfect.
> If a relay driver, with several channels, could do this, it would be a 
> very useful device. Does anything like this exist?
> Thanks,
> Drake
>
> /Drake Chamberlin/
>
> /Athens Electric LLC/
>
> /Ohio Electrical Contractor’s License 44810/
>
> /NABCEP Certified PV Installation Professional/
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260722/b05aedaf/attachment.htm>


More information about the RE-wrenches mailing list