My experience with SW inverters not synced with a cable is that they would
drift to 180 degrees out of sync over a period of about 20 minutes. I could
measure phase to phase and see it go from ~240VAC to 0VAC in that time
frame. In another 20 minutes or so the volts would creep back up to 240
again.
William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
On Wed, Jul 15, 2026 at 6:57 AM
>
>> "Magic Stacking" was when you wired them in 120/240 and used a generator
>> or grid power to sync the output waveforms. That waveform would stay
>> synced for quite some time, days if not weeks, as long as you didn't load
>> them more than 75%. <http://www.members.re-wrenches.org>
>>
>