[RE-wrenches] Balcony Solar
drake.chamberlin at redwoodalliance.org
drake.chamberlin at redwoodalliance.org
Fri May 29 07:10:03 PDT 2026
Home Power Magazine had articles about it, and called it Guerilla Solar.
_Drake Chamberlin_
_Athens Electric LLC_
_Ohio Electrical Contractor's License 44810_
_NABCEP Certified PV Installation Professional_
---
On 2026-05-28 15:10, Jay via RE-wrenches wrote:
> Hi Zeke
>
> I see a few issues.
>
> If there is a circuit with A as the first outlet then B,C,d. If the 16A
> is put into B then C and D now have the potential for 36 amps. Bit high
> for 12 ga wire.
>
> As to the meters as far as I know most all meters unless configured for
> bidirectional use either are mechanical ratcheting so they cant count
> backwards. Or are electronic and I'm unclear as to what happens. I e
> heard they count up either direction so if your selling power the meter
> adds or it might just lock like the ratcheting. I guess depending on
> the meter.
>
> Finally I live in an all electric house and for most of the year, 8+
> months when I'm not using heat, my daytime base loads are like 200
> watts. Of course if someone is home then could be laundry etc.
>
> A small system say 400 watts or less is going to be mostly used for
> some daytime self consumption. But 2000 watts is way overkill and for
> most it seems it will be wasted for the consumer. And as you say it'll
> make people mad about how little it's doing.
>
> Finally as to dates. I had a OK4U made by NKF back in 2000 grid tie
> micro inverter for a single 100 watt panel plugged into an outlet on my
> deck. I keep reading it's a new idea, nope.
>
> Big push lots of hype.
>
>> On May 28, 2026, at 9:40 AM, Zeke Yewdall via RE-wrenches
>> <re-wrenches at lists.re-wrenches.org> wrote:
>
>> Trying to wrap my brain around exactly what this entails.
>> Specifically in Colorado, as that's where I still do most of my design
>> work, but also in other places if it's different/better/worse/etc....
>>
>> This is the actual text of the Colorado bill
>> https://leg.colorado.gov/bill_files/116074/download
>>
>> From reading it... it appears that it's limited to 1920 watts AC
>> output, and limited to one system per address. Systems under 391
>> watts AC output are exempt from a number of other requirements (which
>> seem to pertain mostly to NABCEP certified supervisors and licensed
>> electricians), but still have to be UL listed. Does that imply that
>> licensed electricians or NABCEP certified installers must install ones
>> between 391 watts and 1920 watts?
>>
>> It appears that utilities cannot require approval, a fee, or any
>> modifications to the house electrical system (4a) but can require
>> being notified of the installation and size (4b)
>>
>> I am wondering how this works with ratcheted meters, which is the norm
>> nowadays in Colorado. I have asked Xcel for their guidance on this.
>>
>> In general... the idea of balcony solar seems very problematic. While
>> I'm totally in support of more solar on the grid, and making smaller
>> systems more doable, I have lots of questions on how this will work in
>> reality.
>>
>> 1) Structural issues: Most homeowners do not know how to properly
>> mount solar panels against the winds that we have in Colorado. It's
>> normal for cars and neighbors to be assulted by wandering trash cans
>> during every windstorm... adding errant solar modules to this doesn't
>> seem like a good idea. Most temporary solar racking I've seen from
>> manfucturers (from RV solar sellers mostly) is completely inadequate
>> to withstand 100+mph winds as well. How will proper securing of the
>> solar modules be enforced?
>>
>> 2) Electrical integration: 1920 watts is a fully loaded 20A 120 volt
>> output (16A continuous). If it is a new, high quality outlet, it
>> should be good for that, but what if it is a old outlet on the deck
>> that's gotten all loose from 30 years of power tools and christmas
>> lights being plugged and unplugged? What if it's the $1.99 consumer
>> version of the outlet, not the $8.99 commercial version? I've seen
>> the cheaper ones, and many old loose ones, burn up when used with
>> electric space heaters, which is a similar amperage and time span load
>> to a full size balcony solar system.
>>
>> 3) Metering: Since most all utilities in Colorado now use ratcheted
>> meters, it will be a problem if the system exports without somehow
>> getting a bidirectional meter. If it is a lightly loaded apartment,
>> where a 1920 watt system would really make a different in energy use,
>> then it's likely the baseload will be below 1920 watts midday, and it
>> needs to export. If it's a larger house where the baseload midday is
>> over 1920 watts, then export isn't the issue, but the problem is that
>> people will install a 1920 watt system when they really need a 5 or 8
>> or 12kW system to affect their bill much -- and then they'll just
>> decide that "solar doesn't work" and it will give solar a bad name for
>> more people. Given that most people don't understand kWh and energy
>> use, and marketing always seems to overpromise what equipment can do,
>> I don't expect that a majority of consumers will understand that a
>> 1920 watt system is not sufficient to make a significant impact for a
>> majority of houses out there. I've even had customers install 10kW
>> systems, and not understand that by adding a hot tub and electric
>> water heater and heat pump and electric range at the same time, they
>> overwhelmed the production of the system, and that's why their bill
>> actually went up.
>>
>> 4) Licensure and permits: This could solve some of the issues
>> above... but Colorado allows homeowners to pull permits so licensure
>> and training of the installer is still no guaranteed. And most
>> building departments have a permitting process that's aimed at larger
>> systems... a large system requiring 10 pages of documentation and an
>> engineers stamp and a $500 permit fee is not unreasonable. But for a
>> $2000 balcony kit... how can permitting enforce some basic standards,
>> without becoming a insurmountable hurdle. Also, as a professional
>> installer, I found that fixed costs were a large portion of the cost
>> of installing a system. My cost to do drawings, get a PE stamp for
>> the roof/racking, file for a permit, file for interconnection
>> agreement, and roll a truck were pretty much the same for a 3kW system
>> or a 10kW system. There was more onsite labor for the 10kW system
>> doing racking and modules, but even electrical wiring was about the
>> same onsite labor for both sizes. Onsite labor should be much less
>> for a balcony solar system, especially if plugging into a deck outlet
>> (replacing it with a brand new commercial quality 20A outlet maybe).
>> But costs for drawings, permitting, interconnection won't be different
>> unless a different system is made. Materials are obviously more for
>> the larger systems, but labor made the overall total cost quite a bit
>> higher per watt for the smaller systems, and going to a one or two
>> panel system could be even more share for the off-site labor portion
>> of the total cost. If building departments and utilities put the
>> balcony solar systems through the same paperwork as larger systems, I
>> can easily see that costing more than the materials or onsite labor.
>>
>> --
>>
>> Zeke Yewdall
>> PV Engineer
>> NABCEP #031508-89
>> zeke at darkforestsolar.com
>> 303-523-3592 _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try
>> the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260529/069edcf2/attachment.htm>
More information about the RE-wrenches
mailing list