[RE-wrenches] Code compliant PV wire to an EcoFlow DELTA Pro Ultra Inverter/Charger

Ray Walters ray at solarray.com
Mon Apr 27 19:19:47 PDT 2026


If you look at the graphics on the website, they're really showing 
temporary mounted PV.  This is not designed to be hardwired for an NEC 
approved installation.  It's like a portable generator.  I'd get the guy 
a couple of modules on folding racks, and make up a 50 ft portable cable 
so  he can set the modules in the sun to charge if its a long outage.  
  I've done a few of these for folks, using like the little Jackery 
systems.  Ryobi, Milwaukee, etc make "battery generators"; same 
concept:  you're not going to hardwire them in to anything.  Its got to 
be portable to stay compliant.

If he wants the PV mounted to the roof, you're either throwing code out 
the door, or he needs a different inverter setup.

Ray Walters
Remote Solar

On 4/27/2026 3:36 PM, MDElectricSolar via RE-wrenches wrote:
> What is the input voltage requirement for this PV module to Eco flow 
> unit? It may be a low-voltage input which may not require any metal 
> conduit at all?
>
> Michael D Nelson
> MD Electric & Solar, Inc.
> 707-684-0064 mobile
> 707-884-1862 office
> www.mdelectricsolar.com
> www.facebook.com/mdelectricandsolar
>
>
>> On Apr 27, 2026, at 2:23 PM, Zeke Yewdall via RE-wrenches 
>> <re-wrenches at lists.re-wrenches.org> wrote:
>>
>> 
>> I can't see any way to do this.  Some sort of metal conduit or metal 
>> clad cable (not EMT specifically) is required by 690.31(D)(1) and I 
>> dont think the PVHCS exception would apply to this.   This is an 
>> issue with european style inverters with direct MC4 connectors for 
>> the PV input.
>>
>> Short of putting the entire inverter inside another box, or bolting a 
>> box onto the outside of the inverter that enclosed the MC4 connectors....
>>
>> Zeke
>>
>> Date: Mon, 27 Apr 2026 13:46:25 -0400
>> From: Howie Michaelson <Howie.Michaelson at gmail.com>
>> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> Subject: [RE-wrenches] Code compliant PV wire to an EcoFlow DELTA Pro
>>         Ultra Inverter/Charger
>> Message-ID:
>>         
>> <CAHMeMski8wRM=LnqdqOoPd2AY4oq5w6EddcYpGDvcq_NkJjcDA at mail.gmail.com>
>> Content-Type: text/plain; charset="utf-8"
>>
>> Hi All,
>> I have a potential client who currently has an EcoFlow DELTA Pro Ultra
>> <https://www.ecoflow.com/us/delta-pro-ultra> inverter installed in his
>> house for battery backup.  He wants to install roof-mounted PV. I 
>> don't see
>> how to connect PV into the Inverter/Charger using EMT for code 
>> compliance.
>> Has anyone done something similar?  Can anyone think of a code-compliant
>> method to bring PV into this setup?
>>
>> Howie Michaelson
>>
>> On Mon, Apr 27, 2026 at 1:18 PM 
>> <re-wrenches-request at lists.re-wrenches.org> wrote:
>>
>>     Send RE-wrenches mailing list submissions to
>>     re-wrenches at lists.re-wrenches.org
>>
>>     To subscribe or unsubscribe via the World Wide Web, visit
>>     http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>>     or, via email, send a message with subject or body 'help' to
>>     re-wrenches-request at lists.re-wrenches.org
>>
>>     You can reach the person managing the list at
>>     re-wrenches-owner at lists.re-wrenches.org
>>
>>     When replying, please edit your Subject line so it is more specific
>>     than "Re: Contents of RE-wrenches digest..."
>>
>>
>>     When responding to posts within the Digest, be sure to restore
>>     the Subject: line to the exact original, and please edit out any
>>     extraneous lines from the quoted message.
>>
>>
>>
>>     Today's Topics:
>>
>>        1. Peerless Gas Range Question
>>     (drake.chamberlin at redwoodalliance.org)
>>        2. Code compliant PV wire to an EcoFlow DELTA Pro Ultra
>>           Inverter/Charger (Howie Michaelson)
>>        3. Re: Code compliant PV wire to an EcoFlow DELTA Pro Ultra
>>           Inverter/Charger (Glenn)
>>
>>
>>     ----------------------------------------------------------------------
>>
>>     Message: 1
>>     Date: Mon, 27 Apr 2026 10:09:42 -0400
>>     From: drake.chamberlin at redwoodalliance.org
>>     To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>>     Subject: [RE-wrenches] Peerless Gas Range Question
>>     Message-ID: <b2d629c301707ce64dbd99a52e3911da at redwoodalliance.org>
>>     Content-Type: text/plain; charset="us-ascii"; Format="flowed"
>>
>>
>>     Does anyone know where the spark generator is on a Peerless gas
>>     range?
>>     Tech support can sell us a new one, but can't tell me where the
>>     unit may
>>     be found on the stove.
>>
>>     It may not need a new one. The symptoms are a bit confusing. The
>>     sparkers work well on all burners until the oven is used. After that
>>     they won't work for about 2 days. Then they start working again
>>     until
>>     the oven is used again.
>>
>>     The situation warrants investigation before investing in a new spark
>>     generator.
>>
>>     Thank you,
>>
>>     Drake
>>
>>     _Drake Chamberlin_
>>
>>     _Athens Electric LLC_
>>
>>     _Ohio Electrical Contractor's License 44810_
>>
>>     _NABCEP Certified PV Installation Professional_
>>
>>     --
>>     -------------- next part --------------
>>     An HTML attachment was scrubbed...
>>     URL:
>>     <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260427/c9192082/attachment-0001.htm>
>>
>>     ------------------------------
>>
>>     Message: 2
>>     Date: Mon, 27 Apr 2026 13:46:25 -0400
>>     From: Howie Michaelson <Howie.Michaelson at gmail.com>
>>     To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>>     Subject: [RE-wrenches] Code compliant PV wire to an EcoFlow DELTA Pro
>>             Ultra Inverter/Charger
>>     Message-ID:
>>            
>>     <CAHMeMski8wRM=LnqdqOoPd2AY4oq5w6EddcYpGDvcq_NkJjcDA at mail.gmail.com>
>>     Content-Type: text/plain; charset="utf-8"
>>
>>     Hi All,
>>     I have a potential client who currently has an EcoFlow DELTA Pro
>>     Ultra
>>     <https://www.ecoflow.com/us/delta-pro-ultra> inverter installed
>>     in his
>>     house for battery backup.  He wants to install roof-mounted PV. I
>>     don't see
>>     how to connect PV into the Inverter/Charger using EMT for code
>>     compliance.
>>     Has anyone done something similar?  Can anyone think of a
>>     code-compliant
>>     method to bring PV into this setup?
>>
>>     Howie Michaelson
>>     -------------- next part --------------
>>     An HTML attachment was scrubbed...
>>     URL:
>>     <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260427/871cc0e9/attachment-0001.htm>
>>
>>     ------------------------------
>>
>>     Message: 3
>>     Date: Mon, 27 Apr 2026 14:19:55 -0400
>>     From: Glenn <glenn.burt at glbcc.com>
>>     To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>>     Subject: Re: [RE-wrenches] Code compliant PV wire to an EcoFlow DELTA
>>             Pro Ultra Inverter/Charger
>>     Message-ID: <040db52a-d4c0-46aa-a28d-90a5ce8fb2e3 at email.android.com>
>>     Content-Type: text/plain; charset="us-ascii"
>>
>>     An HTML attachment was scrubbed...
>>     URL:
>>     <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260427/ae1e7f2a/attachment-0001.htm>
>>
>>     ------------------------------
>>
>>     Subject: Digest Footer
>>
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     Pay optional member dues here: http://re-wrenches.org
>>
>>     List Address: RE-wrenches at lists.re-wrenches.org
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>     There are two list archives for searching. When one doesn't work,
>>     try the other:
>>     https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>     List rules & etiquette:
>>     http://www.re-wrenches.org/etiquette.htm
>>
>>     Check out or update participant bios:
>>     http://www.members.re-wrenches.org
>>
>>
>>
>>     ------------------------------
>>
>>     End of RE-wrenches Digest, Vol 19, Issue 128
>>     ********************************************
>>
>>
>>
>> -- 
>> Zeke Yewdall
>> PV Engineer
>> NABCEP #031508-89
>> zeke at darkforestsolar.com
>> 303-523-3592
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try 
>> the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260427/56703ede/attachment.htm>


More information about the RE-wrenches mailing list