[RE-wrenches] Sol-Ark 15K2P F20 MPPT Overcurrent Error

Jason Szumlanski jason at floridasolardesigngroup.com
Sat Apr 11 08:36:15 PDT 2026


You might consider taking this one step further and physically
disconnecting one string at a time. Since the error happens multiple times
a day, maybe you can isolate the issue to one string.


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208




On Fri, Apr 10, 2026 at 7:56 PM david quattro via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> i would swap which strings go into the different MPPT's to see if each
> specific problem follows the DC string // or do they follow the MPPTs.
> Another option is kinda a lot of work but might be worth it - take a
> different inverter out there and "bench test" it with those strings
> unadulterated
> Good luck and please let us how this one resolves.
>
>
>
> On Fri, Apr 10, 2026 at 4:05 PM Vince McClellan via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Hello Wrenches
>> Has anyone else on this list had issues with a Sol-Ark 15K2P randomly
>> shutting down several times a day with an F-20 MPPT overcurrent error? The
>> errors are occurring when the system is well under the max amperage per
>> MPPT of 26 amps. We've had the inverter turn itself off when the online
>> data shows 12.5 amps max. I realize that Sol-Ark's online data updates only
>> every 5 minutes, so I could be possible that there is a spike that the
>> online data isn't showing, but the array is in full sun with the same
>> number of modules and the same string configuration on all 3 MPPT's.
>>
>> We are also seeing other anomalies such as MPPT 1 at 12 amps with MPPT 2
>> and 3 at 22 amps. Again, with the solar array in full sun, no clouds, and
>> no shade.
>>
>> Sol-Ark originally thought it was because of an issue with Tigo RSD
>> switches, but we don't use Tigo. We've had way too many issues with Tigo
>> products.
>>
>> We've had people suggest that we're seeing the results of an edge of
>> cloud affect, but there are not clouds to cause this.
>>
>> We've also tested all the circuits with a insulation tester in every
>> possible configuration, and tested our wiring to insure there were no
>> mistakes by ringing it out with a multimeter. The wiring is good.
>>
>> Sol-Ark tech support doesn't seem to know what the issue is, but they are
>> assuring us that it's not their inverter at fault.
>>
>> I could use any suggestions that come to mind. I'm not sure what else to
>> try at this point.
>>
>> Thank you,
>>
>>
>> Vince McClellan
>>
>> President
>>
>> NABCEP PV Professional
>>
>> p: 541-485-8122
>>
>> a: 860 Conger St. Suite 12,. Eugene, OR 97402
>>
>> e: vince at solarenergydesgin.com
>>
>> w: SolarEnergyDesign.com
>>
>> CCB# 161672
>>
>> If you have received this email and are not the intended recipient,
>> please delete this email. Copying or using any part, content, or attachment
>> of this email is strictly prohibited.
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260411/5bfa88e8/attachment.htm>


More information about the RE-wrenches mailing list