[RE-wrenches] 120/240 Delta
pieter offgridenterprises.org
pieter at offgridenterprises.org
Wed Mar 25 13:01:00 PDT 2026
I would suggest that you confirm the service configuration first. You could have an open Delta, or less likely a high leg delta. Typically ahigh leg Delta will have four current carrying conductors supplying the MDP.
[The Wild Leg]
An open Delta also has a 180 degree relation ship, but is less efficient and you have to be cognizant about creating voltage imbalances.
[https://i.sstatic.net/x5RgQ.jpg]
In either case you have multiple options, but I recommend engaging a PE to help you do it correctly. There is more involved than simply getting the voltages correct.
Pieter Huebner
Project Manager
Off Grid Enterprises
________________________________
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf of Sue Stankevitz via RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Wednesday, March 25, 2026 1:14 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Sue Stankevitz <Sue at midnitesolar.com>
Subject: Re: [RE-wrenches] 120/240 Delta
The Rosie7048RE will do 120/208 with just a setting adjustment.
Sue Stankevitz
MidNite Solar, Inc.<https://www.midnitesolar.com/index.php>
(360) 403-7207 (XT122)
[cid:image001.gif at 01DCBC61.B1521B30]
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Michael Morningstar via RE-wrenches
Sent: Wednesday, March 25, 2026 11:54 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Michael Morningstar <mjmorningstar at gmail.com>
Subject: [RE-wrenches] 120/240 Delta
Wrenches,
I have a customer that has asked me to provide their restaurant with PV and battery back up. Easy-peasy or so I thought. It turns out that the service that supplies the restaurant is being fed by two phases from a 120/240V transformer. The service entrance conductors are direct burial and run under a large paved parking lot, so there's no changing that arrangement. I'm at a loss as what I can do here. I don't believe that something like a Sol-Ark 18k is going to play nice with two legs 120 degrees out of phase? The 30K definitely needs all three phases so a 240 Delta/208 WYE isn't going to help? I don't even think there are micro-inverters or string inverters available to give them just straight grid-tied and no BB. Are there any solutions that I'm unaware of?
Michael
?
--
Michael Morningstar
Morningstar Electric Inc
PO Box 1494
Mount Shasta, CA 96067
530-921-0560
CSLB 1116835
mjmorningstar at gmail.com<mailto:mjmorningstar at gmail.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260325/81eb4e3d/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 4417 bytes
Desc: image001.gif
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260325/81eb4e3d/attachment-0001.gif>
More information about the RE-wrenches
mailing list