[RE-wrenches] Outback FXR Slaves Not Charging With AC
Kirk Herander
kirkh at vermont.solar
Mon Mar 16 08:10:12 PDT 2026
Will the inverter support just 1 master and 3 slave configuration? This
might enable all the slaves to charge.
On Mon, Mar 16, 2026 at 11:01 AM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> The FXR manual supports the way it was installed and configured. There is
> an L1 master and an L2 "subphase master." Each of the slaves is assigned to
> L1 or L2.
>
> And BTW I do have the input mode set to Generator for all four inverters
> (although the slaves take the setting from their masters anyway).
>
>
> Jason
>
>
> On Mon, Mar 16, 2026 at 10:49 AM Steve Higgins <steve at surrette.com> wrote:
>
>> Hey Jason... I'll admit it's been awhile since I was with OB. But from
>> what I remember you can only have one Master inverter.
>>
>> You can't have a master and slave on each leg.
>>
>> The port one inverter needs to be a 1 -2 phase master.
>>
>> The other three should be slave L1 or L2 depending on the phase that they
>> are connected to.
>>
>> My bet is the charging isn't syncing due to the master/slave setup.
>>
>> Right now they aren't backfeeding due to the generator is syncing the
>> phases. I like to call magic stacking. Eventually when the generator
>> isn't running you could see enough drift from that 2nd 1-2 phase master
>> that might cause a backfeed or overcurrent error.
>>
>>
>> *Steve Higgins* *⋅* *Technical Services Manager*
>> *t* +1.902.597.4020 *m* +1.206.790.5840
>> *f* +1.902.597.8447 *e* steve at surrette.com
>> ------------------------------
>> CONFIDENTIALITY: The information transmitted herein is intended only for
>> the addressee and may contain confidential, proprietary and/or privileged
>> material. Any unauthorized review, distribution or other use of or the
>> taking of any action in reliance upon this information is prohibited. If
>> you receive this email in error, please contact the sender and delete or
>> destroy this message and all copies.
>> ------------------------------
>>
>>
>>
>> On Mon, Mar 16, 2026, 7:40 AM Jason Szumlanski via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> I inherited am off-grid service client with four FXR3048A configured in
>>> 120/240 split phase with one master and one slave per leg. I believe I
>>> configured all of the AC input charging parameters correctly, requesting
>>> max charge rate from each inverter. However, when AC input is present (from
>>> a generator) the masters will bulk charge, but the slaves do not charge at
>>> all. The slaves do share the load, but show 0.0kW for charging.
>>>
>>> Any ideas?
>>>
>>> Jason Szumlanski
>>> Florida Solar Design Group
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
*Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
*Owner|Principal, VT Solar, LLC*
*Celebrating our 35th Anniversary 1991-2026!!*
dba Vermont Solar Engineering
802.559.1225
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260316/8a1653f5/attachment.htm>
More information about the RE-wrenches
mailing list