[RE-wrenches] Outback FXR Slaves Not Charging With AC
Jay
jay.peltz at gmail.com
Mon Mar 16 06:19:16 PDT 2026
I haven’t installed too many of the A versions so might be different but the yellow led acinput lights on the inverters should be solid on when it’s connected to the acinput. Flashing when it’s thinking about connecting.
And you mention a led is flashing?
> On Mar 16, 2026, at 6:58 AM, Jay <jay.peltz at gmail.com> wrote:
>
>
> And you set each inverter ac input amps as well?
>
> Jay
>
>>> On Mar 16, 2026, at 6:40 AM, Jason Szumlanski via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>
>> I inherited am off-grid service client with four FXR3048A configured in 120/240 split phase with one master and one slave per leg. I believe I configured all of the AC input charging parameters correctly, requesting max charge rate from each inverter. However, when AC input is present (from a generator) the masters will bulk charge, but the slaves do not charge at all. The slaves do share the load, but show 0.0kW for charging.
>>
>> Any ideas?
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260316/b9ee9cb2/attachment.htm>
More information about the RE-wrenches
mailing list