[RE-wrenches] Is this city inspector just full of it? His comments and my response. City is on NEC 2023

scot.arey at solarcentex.com scot.arey at solarcentex.com
Sat Mar 7 13:44:48 PST 2026


You have identified a good friction point. A code inspector might say '705, blah blah...690 says it deals with "array circuit (s), inverter (s), and..." '

But I think you are absolutely right to look at 705 for "Wiring Methods." The paragraph (C) covers the Enphase MC cable but it is (A) that says can use wiring methods approved elsewhere in code and that means Chapter 3.

Phew...

[cid:8d7fa9ec-b3f4-4c6c-9412-823a4dff36b8]



Howard "Scot" Arey
Owner, Solar CenTex
254-300-1228

________________________________
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf of Zeke Yewdall via RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Saturday, March 7, 2026 10:16 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Zeke Yewdall <zeke at darkforestsolar.com>
Subject: Re: [RE-wrenches] Is this city inspector just full of it? His comments and my response. City is on NEC 2023

I think he's having trouble with the definitions of different circuits.

Figure 705.1 shows a diagram showing where the inverter output circuit is, which is what he's talking about, not a PV output circuit or a PV source circuit, which is what most of 690 addresses, and are shown in the figures in 690... however it is confusing when they throw in current rating for an inverter output circuit in 690.8.

I can't quickly find any references to requirements for inverter output circuits, other than all of the stuff in 705 about interconnecting them.

The language about the over 150 volts to ground is from 690.7(D) back in 2011... not sure when they removed it, but it's not in the 2020, 2023, or 2026 books I have handy....

Zeke

On Fri, Mar 6, 2026 at 9:07 PM <re-wrenches-request at lists.re-wrenches.org<mailto:re-wrenches-request at lists.re-wrenches.org>> wrote:
Send RE-wrenches mailing list submissions to
        re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>

To subscribe or unsubscribe via the World Wide Web, visit
        http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
or, via email, send a message with subject or body 'help' to
        re-wrenches-request at lists.re-wrenches.org<mailto:re-wrenches-request at lists.re-wrenches.org>

You can reach the person managing the list at
        re-wrenches-owner at lists.re-wrenches.org<mailto:re-wrenches-owner at lists.re-wrenches.org>

When replying, please edit your Subject line so it is more specific
than "Re: Contents of RE-wrenches digest..."


When responding to posts within the Digest, be sure to restore the Subject: line to the exact original, and please edit out any extraneous lines from the quoted message.



Today's Topics:

   1. Is this city inspector just full of it? His comments and my
      response. City is on NEC 2023 (scot.arey at solarcentex.com<mailto:scot.arey at solarcentex.com>)


----------------------------------------------------------------------

Message: 1
Date: Sat, 7 Mar 2026 03:29:56 +0000
From: "scot.arey at solarcentex.com<mailto:scot.arey at solarcentex.com>" <scot.arey at solarcentex.com<mailto:scot.arey at solarcentex.com>>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>>
Subject: [RE-wrenches] Is this city inspector just full of it? His
        comments and my response. City is on NEC 2023
Message-ID:
        <BYAPR02MB4086C40A4CCA00A78023A4C0F27BA at BYAPR02MB4086.namprd02.prod.outlook.com<mailto:BYAPR02MB4086C40A4CCA00A78023A4C0F27BA at BYAPR02MB4086.namprd02.prod.outlook.com>>

Content-Type: text/plain; charset="utf-8"

Read and reply only if you want to stick it to an inspector ?

System is 19 modules with Enphase IQ8: NM through attic and he insists it must be guarded or in conduit. His comment back to me on why he failed the inspection and I tried to tell him that the IQ8 output is not a PV source circuit.


Good afternoon,  I have just read your email and would like to inform you that your code reference is spot on.  690.6 A PV Source Circuit refers to a NRTL  Listed assembly and is exclusive to the wiring from the Panel to the Microinverter, it as a listed assembly is not subject to the DC rules of 690..  690.6 b refers to the Inverter Output Circuit and is not exempt from the rules of 690.7 Circuit Requirements, Specifically D which states, ?Circuits over 150 volts to ground. In one and two family dwellings, live parts in PV source circuits and PV output circuits over 150 volts to ground Shall Not be accessible to other than qualified persons while energized.  The commentary for this code states, Conduit, closed cabinets, or enclosures that require tools to open them are means of limiting access to qualified persons only.  These circuits are production and not utilization circuits and therefore must be protected from physical damage and errant tampering.  As was noted at Plan Review

Dd

My proposed response:

I have read your reply and believe you have mis-cited code references. You wrote:

"690.6 b refers to the Inverter Output Circuit and is not exempt from the rules of 690.7 Circuit Requirements, Specifically D which states, ?Circuits over 150 volts to ground. In one and two family dwellings, live parts in PV source circuits and PV output circuits over 150 volts to ground Shall Not be accessible to other than qualified persons while energized."

690.6b is here.
[cid:1554f576-5063-4098-a38c-3a8291b6699d]
690.7 (D) does not reference "circuits over 150-volts..." but is pasted here. This is a reference to marking of direct current (DC) PV circuits. This does not apply because the inverter output circuit is not a "DC PV Circuit."

[cid:5e6c0708-cbd2-4be2-82c4-44f97a1db3d2]
________________________________


The section that almost refers to "PV output circuits over 150 volts to ground Shall Not be accessible" is not in NEC 2023 which is what Temple uses. I have pasted the 2020 language, which is not the language you cite to me, and even that is referring to "PV source and output" circuits and the NEC  2020 definition of "PV source and output" deals with DC. I have pasted and highlighted that definition below.

[cid:407b334f-2b4d-4975-8f4a-22d82c45293c]



[cid:2f2cd9f6-90e8-4b1e-a1d6-62dbf28e2fd0]
[cid:fb85f1f2-2846-4c4a-807c-b3085e9bbe29]


So we are left with the fact that an inverter output circuit is alternating current, as defined under NEC 2023. Definition in Section 100:

[cid:4bd3f0a1-dd27-4c5b-a5c7-335f132f38cd]


We are left with Chapter 3 wiring to address this AC circuit. There is no NEC 2023 reference to "These circuits are production and not utilization circuits and therefore must be protected from physical damage and errant tampering." Simply not in code.

If you insist I put the AC wire in conduit, please tell me the requirement. If it's "I just want it in conduit" then just ell me that. But there is little to justify it in NEC 2023.





Howard "Scot" Arey
Owner, Solar CenTex

NABCEP PV Installation Professional
TECL 29755
254-300-1228
[cid:f2ce8538-438b-48d0-92e0-1e00d98cc434]

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260307/e006f320/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 136049 bytes
Desc: image.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260307/e006f320/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 1134546 bytes
Desc: image.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260307/e006f320/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 470202 bytes
Desc: image.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260307/e006f320/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 46022 bytes
Desc: image.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260307/e006f320/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 193618 bytes
Desc: image.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260307/e006f320/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 414241 bytes
Desc: image.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260307/e006f320/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-dzzqmyah.png
Type: image/png
Size: 294949 bytes
Desc: Outlook-dzzqmyah.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260307/e006f320/attachment-0006.png>

------------------------------

Subject: Digest Footer

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



------------------------------

End of RE-wrenches Digest, Vol 19, Issue 75
*******************************************


--
Zeke Yewdall
PV Engineer
NABCEP #031508-89
zeke at darkforestsolar.com<mailto:zeke at darkforestsolar.com>
303-523-3592
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260307/ec98eddd/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 370122 bytes
Desc: image.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260307/ec98eddd/attachment-0001.png>


More information about the RE-wrenches mailing list