[RE-wrenches] 600VDC 3 Phase Inverters

William Miller william at millersolar.com
Mon Feb 23 12:15:04 PST 2026


Travis:

This is the classic “repowering” dilemma. Low voltage string wiring versus
new 1000 or 1500 VDC inverters.

We used CPS 60 K inverters and bypassed the on-board combiner. The CP60
will operate at lower string voltages.

The inverters are operating somewhat outside the most efficient parameters
but the system is working reliably.

Here is a link to the case study:

https://millersolar.com/MillerSolar/case_studies/30-Re-Powering/re-powering.html


Good luck.

William Miller
Miller Solar.com
805-438-5600
www.millersolar.com


On Mon, Feb 23, 2026 at 11:42 AM Travis Knipple via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Hi wrenches,
> I've got a service call that needs a ~50kVA inverter, 3 phase (could be
> 208 or 480)
> I'm replacing an older system, and the existing stringing is set up with:
> 3 strings, with each strings calculations ending up at:
> ~359Vmp (Hottest Conditions)
> -510Voc (Cold)
> 40A Imp, 42.8A Isc
>
> So, I'm hitting 2 issues:
> (A) Vmp too low for many newer inverters
> (B) Newer inverters want to land each string individually, and this system
> merged the strings in DC Cominers at the array, so I would prefer to give
> the 40A input to 1 terminal if possible to avoid a 300' repull. (I have 3
> pairs of #4, and would have to repull 15 pairs of #10. It's possible, but
> not preferred)
>
> If anyone has a brand of inverters I should investigate that may work,
> please let me know.
> Thanks,
> Travis
>
> --
> Travis Knipple
> Senior Engineer
> Hudson Solar Solutions LLC
> Rhinebeck, NY 12572
> 518-539-8040 x408 | travis at hudsonsolarsolutions.com
>
> PVIP# PV-111821-013612
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260223/02c0309a/attachment.htm>


More information about the RE-wrenches mailing list