[RE-wrenches] Q.PEAK DUO BLK-G6+ underproduction
Dave Tedeyan
dave at sungineersolar.com
Wed Feb 11 06:26:13 PST 2026
I must admit, this is a little embarrassing... this is what I get for
trying to work with a head cold. I didn't remember that there was a change
order on this one, and the original contract was for a larger system than
what eventually got installed. I was looking at the producion estimate from
the original larger system, which was around 17MWh/year. The actual
production estimate is closer to 14.3MWh, and the system has averaged
13.5MWh over the past 5 years. So, 94% is not nearly as bad as I originally
thought, although it is still not good either.
The voltages that I am seeing on the Sunny Portal monitoring are still
lower than I would expect. I think it is still worth checking out with an
IR scan once the snow goes away and the sun comes back here in upstate NY.
The recommendations for doing a curve trace would be the best
troubleshooting step, although I have not yet invested in one of those. All
this still leads me to believe that these Qcell modules may be not quite be
performing to spec, but they are not as ridiculously far off as I feared.
Cheers,
Dave
On Tue, Feb 10, 2026 at 8:50 PM Roy Rakobitsch via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> It would be fairly easy to spot bypass diode issues or cell current
> imbalance issues with a hand-held IR imager on a decently sunny day. Maybe
> time to go on the roof and take a peek?
>
>
> Roy Rakobitsch
>
> Windsine LLC
> 631-514-4166
>
> On Tue, Feb 10, 2026, 18:25 Jay via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Looking at it from performance ie watts, how far off does it appear to be?
>>
>> Jay
>>
>>
>>
>> On Feb 10, 2026, at 2:07 PM, Dave Tedeyan via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>
>> Hi All,
>>
>> I was just reviewing a site installed about 5 years ago and am finding it
>> is not doing nearly as well as I would have expected. Most of our sites
>> produce relatively close to our projections, but this one is pretty far
>> off. There are 3 strings of 12 Q.PEAK DUO BLK-G6+ modules. Two strings go
>> to a 7.7kw inverter and one string goes to a 3.8kw inverter - both of which
>> are the -41 series SMA inverters. There are Tigo TS4-R-F rapid shutdown
>> devices on all the modules.
>>
>> Vmp for 12 of these panels should be about 407V at STC. At 50C (which is
>> really hot for upstate NY), the Vmp should be around 380V. On a perfect
>> summer day, I am seeing Vmp of around 320V. On a perfect spring day
>> (cooler, with some power clipping, I am seeing Vmp of around 355V. And on a
>> perfect winter day (when there was no snow) Vmp is around 365V. All three
>> strings are pretty consistent with each other, so I don't think that there
>> are specific installation issues with any panels, unless we managed to
>> forget to wire in two panels in all three strings which is extremely
>> unlikely.
>>
>> So, I can only think of two things that might be at play here:
>> 1. Maybe these modules are just crap, and are not at all performing to
>> spec.
>> 2. Maybe the Tigo devices are causing issues.
>>
>> Has anyone out there experienced production issues like this? Everything
>> appears normal, it is on an open rooftop, and there are not things like
>> partial shading, weeds, bird poop, or other soiling affecting the modules.
>> I don't have another site with the same modules that also has good
>> monitoring data, but maybe some of you do!
>>
>> Thanks for the consideration!
>> Cheers,
>> Dave
>> --
>>
>> Dave Tedeyan, P.E.
>> Owner | Sungineer Solar
>> p: he | him | his
>> a: 1653 Slaterville Rd. | Ithaca, NY 14850
>> w: www.sungineersolar.com <http://www.sungineersolar.com/>
>> c: (607) 270-0370
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260211/ea272326/attachment.htm>
More information about the RE-wrenches
mailing list