[RE-wrenches] Will IQ8 microinverters backfeed a generator during grid interruptions

Dave Angelini Offgrid Solar offgridsolar at sti.net
Tue Jan 27 10:02:28 PST 2026


The failsafe for me offgrid, is the owner has to know how to do these 
things. I say bye bye if they are not capable. Sleep really well with 
the independance concept.

Dave Angelini Offgrid Solar
"we go where powerlines don't"
    [2]https://offgridsolar1.com/ [3]  [2]
e-mail  offgridsolar at sti.net
text 209 813 0060

On 2026-01-27 9:14 am, Jason Szumlanski via RE-wrenches wrote:

> I don't like to install anything that isn't failsafe for this purpose, 
> so if it relies on a NC relay opening upon receiving generator voltage, 
> I usually won't consider it because the relay can fail. And if the 
> relay fails, there is no indication of that (other than the adverse 
> effects that might happen).
> 
> That's just my opinion, but I can understand fringe scenarios where 
> there just isn't a way to get the solar connected on the line side. As 
> long as the customer signs off on the risks, I would do it, but 
> cautiously.
> 
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
> 
> On Mon, Jan 26, 2026 at 4:41 PM Howard Scot Arey via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Interesting. Somebody else recommended a web-based version of what you 
> did. You were ahead of the times. I might pursue this with the web 
> option...not the radios. Same concept - different technology.
> 
> Thank you.
> 
> Howard "Scot" Arey
> Owner, Solar CenTex
> 
> NABCEP PV Installation Professional
> TECL 29755
> 254-300-1228
> 
> -------------------------
> 
> From: William Miller <william at millersolar.com>
> Sent: Monday, January 26, 2026 3:28:04 PM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Cc: scot.arey at solarcentex.com <scot.arey at solarcentex.com>
> Subject: RE: [RE-wrenches] Will IQ8 microinverters backfeed a generator 
> during grid interruptions
> 
> Friends:
> 
> I had the same problem:  Enphase arrays on an outbuilding which was 
> connected to the generator side of a transfer switch.  I had no 
> independent power path from the grid to the outbuilding so the Enphase 
> had to be connected to the load side of the transfer switch.  When the 
> large generator was powering the facility and the sun was out the 
> generator acted wonky (unstable voltage).
> 
> My solution was to buy a transceiver set (National Control Devices 
> MlrXR2x).  I powered one radio from the grid side of the transfer 
> switch and the other radio controlled a contactor on the remote Enphase 
> feeders.  When the grid goes down the contactor opens.
> 
> The radios were inside of two buildings and the reception was 
> borderline.  I augmented the included 900 mHz rubber duckies by 
> replacing them with panel antennas from Pasternak.  So far the system 
> is operating as intended.
> 
> If anyone wants details let me know.
> 
> William
> 
> William Miller
> 
> Miller Solar
> 
> www.millersolar.com [1]
> 
> CA License C-10 77398
> 
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On 
> Behalf Of scot.arey--- via RE-wrenches
> Sent: Wednesday, January 21, 2026 12:45 PM
> To: RE-wrenches
> Cc: scot.arey at solarcentex.com
> Subject: Re: [RE-wrenches] Will IQ8 microinverters backfeed a generator 
> during grid interruptions
> 
> Thanks but I'm just trying to grid-tie a small Enphase array without 
> ESS where the point of interconnection is on the customer side of the 
> generator/ATS.
> 
> Trying to use existing wires in place to simplify and lower costs...but 
> the generator is my constraint because I need the PoI to be on line 
> side of the ATS.
> 
> Howard "Scot" Arey
> 
> Owner, Solar CenTex
> 
> 254-300-1228
> 
> -------------------------
> 
> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf 
> of Jason Szumlanski via RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Sent: Wednesday, January 21, 2026 2:33 PM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Cc: Jason Szumlanski <jason at floridasolardesigngroup.com>
> Subject: Re: [RE-wrenches] Will IQ8 microinverters backfeed a generator 
> during grid interruptions
> 
> I should have also noted that Enphase DOES allow use of a generator 
> with its System Controller 3G, and supposedly the inverter, battery, 
> and generator sources can all power loads simultaneously, so I could be 
> wrong about how the IQ8s work. That said, Enphase has strict pairing 
> specifications and an approved generator list. They seem confident in 
> their ability to limit backfeed to the generator in this scenario.
> 
> Jason Szumlanski
> 
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> 
> Florida Certified Electrical Contractor EC13013208
> 
> On Wed, Jan 21, 2026 at 3:16 PM William Bryce via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> If the AC coupled exported energy is more than the generator produced 
> energy, it can destroy the generator controller.
> 
> That is why most AIO inverters have a relay on the dedicated AC 
> coupling input. It will open the relay if the inverter sees generator 
> power.
> 
> The MNP AIO will allow both inputs, but will open the relay if the AC 
> coupled power increases to 20% of the Generator input (firmware 
> dependent).
> 
> On Wed, Jan 21, 2026 at 2:27 PM Jason Szumlanski via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Enphase IQ8 microinverters will absolutely leak some power back to the 
> grid when set to a no-export grid profile. How much, and if that is 
> detrimental to the generator is another question. I suspect if the 
> generator is large enough relative to the PV array, the impact will be 
> nil, but I would not take the risk.
> 
> I don't think the fast switching really does the trick in terms of not 
> exporting. That function relies on the consumption CTs connected to the 
> Gateway, which in turn communicates with the microinverters. Aside from 
> the CTs not being totally accurate, I don't see how that communication 
> loop could be fast enough.
> 
> Jason Szumlanski
> 
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> 
> Florida Certified Electrical Contractor EC13013208
> 
> On Wed, Jan 21, 2026 at 12:09 PM scot.arey--- via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Good day,
> 
> I many years ago watched the fast-switching capabilities of the IQ-8 
> microinverters to produce only what demanded of the MI, and wondered if 
> it might have application in a grid-tied system that is served by a 
> whole-house generator.
> 
> We have the opportunity to install grid-tied-only array of 24 IQ8 but 
> all the MIs will be on the customer side of an auto-transfer switch and 
> generator. We want to leverage using existing building wiring to carry 
> the solar and all solar sizing meets the 120% rules.
> 
> But I know that grid-tied solar on the customer load-side of the 
> transfer switch means no place for full solar power production to flow 
> to when the grid is not available...but  then I thought back to that 
> fast switching capability: is there a way to ensure the IQ8 don't 
> backfeed a generator when it is operating for a grid anomaly?
> 
> I suspect the answer is "are you nuts???" but that video of capability 
> got me thinking, "why not?" and if not, how is it - what tells the MI 
> to cease production? - when it is within a full and proper ISC/ESS 
> system design?
> 
> Howard "Scot" Arey
> 
> Owner, Solar CenTex
> 
> NABCEP PV Installation Professional
> 
> TECL 29755
> 
> 254-300-1228
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
------
[1] http://www.millersolar.com/
[2] http://members.sti.net/offgridsolar/
[3] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260127/521ab233/attachment-0001.htm>


More information about the RE-wrenches mailing list