[RE-wrenches] Ferrules for large fine-stranded wire.

William Miller william at millersolar.com
Sun Jan 25 16:38:42 PST 2026


Jay:



It is 34 gauge, as close as I can measure.  I bought it decades ago at a
local hobby shop that is long gone.  A quick search shows me its available
on Etsy and likely many other places.



William



William Miller

Miller Solar

www.millersolar.com

CA License C-10 77398



*From:* Jay [mailto:jay.peltz at gmail.com]
*Sent:* Sunday, January 25, 2026 4:05 PM
*To:* william at millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Ferrules for large fine-stranded wire.



Hi william



Can you tell us what thickness this is and is it something you’ve ordered
on line or where to get it



Thx

Jay



On Jan 25, 2026, at 2:34 PM, William Miller via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:



Kirk:



It is fortuitous you would write on the subject when you did.  I was
connecting an Envy inverter at that moment.



We have settled on the copper sheeting method:  We cut a strip of thin
copper sheeting to wrap about 1-1/2 times around the bare strands, insert
the conductor in the screw lug and tighten to the specified torque.  I have
done this multiple times over decades without failure.  We sometimes take
the cable back out of the lug to inspect.  All indications are this
technique is acceptable.  This solution is inexpensive and portable.



William



William Miller

Miller Solar

www.millersolar.com

CA License C-10 77398



*From:* Kirk Herander [mailto:kirkh at vermont.solar]
*Sent:* Friday, January 23, 2026 9:44 AM
*To:* william at millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Ferrules for large fine-stranded wire.



William, All,



I was at a workshop on the (sort of) new Fortress battery product the other
day. I brought up this very

issue of the terminal lugs of the Envy not accepting a 4/0 ferrule, even
though 4/0 cable with ferrules are recommended in the manual. The
instructor had no comment, except to imply that maybe one should use 3/0
max. Huh?



Anyway these Greaves pin adapters are by far the best I've found for
working with the 4/0 terminal block.

The pin diameter matches 4/0 cable and thus fits great. Preferable IMO to a
reduced 4/0 barrel to 2/0 pin of AL or AL-clad others. And the barrel has a
generous flange which makes it quite easy to insert high-strand flex cable.

#PT 222FX40. But @ $50 ea, not cheap.



<image003.png>



On Wed, Sep 3, 2025 at 7:10 PM William Miller via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

Friends:



My understanding is if the lug has a set-screw that contacts the strands,
fine strands can wind around the set screw, get into the threads and not
tighten adequately.  If you are crimping fine strands inside of some type
of barrel your connection should be OK.



I had been using Outback until they imploded and all of the battery
connections were via studs or bolts that required crimped-on rings.  Now I
am back to set screw lugs and fine stranding became an issue again.



I did try another experiment: I took a 4/0 ferrule that would not fit into
the Envy lugs and snipped a section out of it.  I curled it into a slightly
smaller diameter and it fit into the lug.  I suppose one could cut the
ferrule in half longitudinally and insert a portion of the ferrule between
the set screw and the strands.



I am pleased with the copper sheeting wrapped around the fine strands.
That will be my SOP.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Ray Walters via RE-wrenches
*Sent:* Wednesday, September 3, 2025 1:40 PM
*To:* re-wrenches at lists.re-wrenches.org
*Cc:* Ray Walters
*Subject:* Re: [RE-wrenches] Ferrules for large fine-stranded wire.



I've got to ask: Are none of the lugs on these Chinese inverters approved
for fine strand cable?  I just have not had a problem with that, but I've
mostly used Magnum, Midnite, and Outback equipment over the years.   What
were the lugs on the old Trace DC 250 boxes?  Were they fine strand rated?
They sure were tough to get 4/0 into, as William mentioned.

Ray
Remote Solar

On 9/3/2025 12:57 PM, Kent via RE-wrenches wrote:

William,

If the only reason the ferrule wouldn't fit after using the hex crimper was
the ridge left where the dies meet, you could rotate the cable 120 degrees
and crimp the ferrule again.

I doubt that the indenter crimper will do a decent job with large ferrules.

I do like your thin piece of copper solution. Not UL approved but I dare
say wrench approved.

Kent Osterberg
Blue Mountain Solar



On 9/2/2025 8:55 PM, William Miller via RE-wrenches wrote:

Friends:



Thank you for all of your input on this question.  I feel it only right I
report back how this turned out



I tried a crimper like this:







It left a jagged ridge on both sides of the ferrule where the dies met.



The crimper below was suggested but I have not tried it:



This was suggested but I have not tried it either:





_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org




-- 



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260125/27cf25b0/attachment.htm>


More information about the RE-wrenches mailing list