Enphase IQ8 microinverters will absolutely leak some power back to the grid
when set to a no-export grid profile. How much, and if that is detrimental
to the generator is another question. I suspect if the generator is large
enough relative to the PV array, the impact will be nil, but I would not
take the risk.
I don't think the fast switching really does the trick in terms of not
exporting. That function relies on the consumption CTs connected to the
Gateway, which in turn communicates with the microinverters. Aside from the
CTs not being totally accurate, I don't see how that communication loop
could be fast enough.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Wed, Jan 21, 2026 at 12:09 PM scot.arey--- via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Good day,
>
> I many years ago watched the fast-switching capabilities of the IQ-8
> microinverters to produce only what demanded of the MI, and wondered if it
> might have application in a grid-tied system that is served by a
> whole-house generator.
>
> We have the opportunity to install grid-tied-only array of 24 IQ8 but all
> the MIs will be on the customer side of an auto-transfer switch and
> generator. We want to leverage using existing building wiring to carry the
> solar and all solar sizing meets the 120% rules.
>
> But I know that grid-tied solar on the customer load-side of the transfer
> switch means no place for full solar power production to flow to when the
> grid is not available...but then I thought back to that fast switching
> capability: is there a way to ensure the IQ8 don't backfeed a generator
> when it is operating for a grid anomaly?
>
> I suspect the answer is "are you nuts???" but that video of capability got
> me thinking, "why not?" and if not, how is it - what tells the MI to cease
> production? - when it is within a full and proper ISC/ESS system design?
>
>
>
> *Howard "Scot" Arey*
> *Owner, Solar CenTex*
>
> NABCEP PV Installation Professional
> TECL 29755
> 254-300-1228
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260121/eb1b45f1/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-cjrhro0j.png
Type: image/png
Size: 294949 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260121/eb1b45f1/attachment-0001.png>
More information about the RE-wrenches
mailing list