[RE-wrenches] Battery Sensor Light on VFX3648

Chris Schaefer chris at solarandwindfx.com
Fri Jan 9 15:35:43 PST 2026


While on the subject of VFX inverters in regards to the fan and internal
temp sensors, I've got a client with a circa 2010 VFX3624 that appears to
have a failed fan. I don't normally deal with 24 volt inverters. I've got
many dead VFX3648 units hanging out. My question is can I cannibalize a fan
out of a 48 volt unit and put it in a 24 volt unit? Next, let's say the fan
is ok and based on the readings above I should look into replacing the xfmr
temp sensor. Again, can I take one out of a 48v inverter and use it on a
24v unit? Which board might be suspect as well that the xfmr temp sensor
feeds its information too?

Thanks,
Christopher

On Thu, Jan 8, 2026 at 9:23 PM Jerry Shafer via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Wrenches, Jay,
> Transformer temp sensors in the FX Fails, fans fail causing fet boards to
> overheat, dirty filters cause high temps on all the intervals. When outback
> was still running the parts department you always got temp senders with
> fans, boards and a relocation procedure, yes you must put the sensor in a
> new location.
> FunTimes
>
> On Thu, Jan 8, 2026, 3:26 PM Jay via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> I’ve replaced dozens of internal temp sensors over the years.
>>
>> I learned to also replace the fan at the same time.
>>
>> Or vice versa.
>>
>> Jay
>>
>> On Jan 8, 2026, at 4:01 PM, Luke Christy via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>> Drake,
>> I agree with Ray,
>> The message you’re seeing does not refer to the RTS that has been absent
>> for years- it’s an issue with an internal sensor.
>> I have seen intermittent warnings relating to internal sensors on VFX
>> units that have self-resolved with a reboot, but if the warning is
>> persistent then you’ll likely need to open the unit up and replace the
>> sensor.
>>
>> Luke Christy
>> Renewable energy consultant
>>
>> NABCEP Certified PV Installation Professional™:
>>
>> Solar Gain Services, LLC
>> PO Box 531
>> Monte Vista, CO 81144
>> 719.588.3044
>> sgsrenewables at gmail.com
>>
>> On Jan 8, 2026, at 3:00 PM, Drake Chamberlin via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>> A couple of years back, a client changed from lead acid batteries to
>> LiFeBlue, lithium batteries. At that time the temperature sensor was
>> removed.
>>
>> The other day, a warning light started blinking. The warning turned out
>> to be a bad temperature sensor. It is strange that this message showed up
>> now, as the sensor has been gone for years.
>>
>> Is there any way to turn off the warning light?
>>
>> Thank you,
>>
>> Drake
>>
>>
>> *Drake Chamberlin*
>>
>> *Athens Electric LLC*
>>
>> *Ohio Electrical Contractor’s License 44810*
>>
>> *NABCEP Certified PV Installation Professional*
>>
>>
>> --
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

Chris Schaefer’s


*Tel 585-229-2083 or Cell 585-748-1870 *
*5115 S Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
<chris at solarandwindfx.com>*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260109/d2528ad7/attachment.htm>


More information about the RE-wrenches mailing list