[RE-wrenches] FLA battery problelm

Michael Morningstar mjmorningstar at gmail.com
Fri Dec 12 10:31:13 PST 2025


Chronic undercharging, electrolyte dilution, lack of informed equalization,
and adding water without knowledge of the how’s, whys, and when’s will kill
those batteries in no time. I’ve pulled out to many of those heavy bastards
to count, most of them at a fresh young  age because the installer didn’t
educate the clients properly.


On Fri, Dec 12, 2025 at 10:21 AM David Coale via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Hi Wrenchers,
>
> I have a client with an old off-grid Trace system and he is having trouble
> with the batteries.  He has HUP Solar One FLA batteries that are about 4
> years old, so they should be in good shape.  The last set lasted almost 20
> years with a fair amount of abuse.
>
> Here is he history and what I think is going on. 7/21 they got new
> batteries after about 19 years of use.
>
> 7/22 I get a call saying the batteries are not charging up all the way.
> When I check out the system, the batteries needed cleaning, and I found
> three low cells, and the charger settings were back to default, not set
> high enough to charge the batteries all the way (it’s always multiple
> problems).  The client (now a new renter, new to the system) said he was
> filing the batteries once a month and experienced some overflowing when the
> batteries were charged up.
>
> I cleaned things up, reset the charging parameters and set up an
> equalizing charge to even out the cells. Hopefully this will fix things.
>
> 11/25. The client calls and said the batteries don’t charge up all the way
> and he is running the generator a lot and worried about getting though the
> wintertime.
> When I check things out, there are three bad cells and there is soda on
> the batteries. It is hard to get a good voltage readings because of the
> soda. Most of the cells are reading 2.1 volts under about a 40 amp load.
>
> Yesterday I check things out, and all the cells are reading between 1.93
> to 1.98 under a 40 amp load in the morning, and I don’t find any bad
> cells.  The charging voltage is never going over about 52 volts so the
> system is never getting fully charged up.  The charge setting look OK, so
> not sure what is going on. This is acting like an old battery pack but
> these batteries are relatively new.
>
> My guess at this point is that maybe the batteries lost acid with the
> overflowing event and lost capacity.  Maybe adding acid back in would bring
> them back up to working order.  The SG measured at 1.150 or less.
>
> At this point the client (renter) has had enough of these battery problems
> and is wondering every morning if the batteries will last long enough to
> until the sun comes up.  The renter is pushing for a replacement LFP
> battery, but there should be lots of life left in this battery pack.
>
> Let me know what you all think.
>
> Thanks,
>
> David
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --

Michael Morningstar


Morningstar Electric Inc

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

CSLB 1116835

mjmorningstar at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20251212/31868b16/attachment.htm>


More information about the RE-wrenches mailing list