[RE-wrenches] Disable refloat
Starlight
larry at starlightsolar.com
Fri Dec 12 08:10:56 PST 2025
Hello Drake,
Absorption is the phase where voltage remains constant. Until the Absorb voltage value is achieved, you will be bulk charging. You can only force Float or Bulk.
Larry Crutcher
Starlight Power Systems
On Dec 12, 2025, at 8:58 AM, Drake Chamberlin via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
Hi Jay,
The system feeds the grid through an SMA H-FUS inverter. The Outbacks are off grid inverters, but are AC coupled to the batteries to provide power when the grid is down.
The inverters monitor the batteries and go into REFLOAT when the batteries hit 25 volts. I would like the inverters to go strait into the ABSORB cycle instead of going to REFLOAT.
The grid tie came after the the Outbacks were already in as a backup system.
Thank you,
Drake
Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor’s License 44810
NABCEP Certified PV Installation Professional
---
On 2025-12-11 10:54, Jay via RE-wrenches wrote:
>
> Hi drake.
>
> You’re talking about the inverters charging the battereis, meaning
> this is a grid connected system?
>
> Do you have a mate3/s or 1?
>
> Jay
>
>> On Dec 11, 2025, at 7:39 AM, Drake Chamberlin via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>
>>
>> Hello Wrenches,
>>
>> We have a rental property with two, stacked VFX 3524 inverters. In the winter the batteries don't get an adequate solar charge. I would like to have the batteries get a bulk charge when the voltage drops to 24 volts, but it keeps hitting refloat.
>>
>> How do I disable refloat? Can I just set the refloat time to zero?
>>
>> Thank you,
>>
>> Drake
>>
>> --
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20251212/c62fdab9/attachment.htm>
More information about the RE-wrenches
mailing list