[RE-wrenches] N-G bond for supply side connection Midnite Power
Dave Tedeyan
dave at sungineersolar.com
Thu Oct 23 17:58:12 PDT 2025
Thanks all for your thoughts here. It seems that the general consensus so
far is that the N-G should be bonded in the solar main disconnecting means
when doing a supply side connection (even if it is not technically a
separate service). When talking with Midnite Power, we made it very clear
that we were talking about a N-G bond in the inverter combiner / solar main
disconnect, and not the backed up loads panel. And being that NY is still
on 2017 code (only going to 2020 next year), with the ambiguity in the code
I am probably okay to undo the N-G connection in the main solar disconnect.
In this case specifically, we are backing up only a small subset of loads
in the house. The reason for the two inverters is because there is about
24kw of solar. There is also a manual transfer switch to normally be able
to power the loads off the inverters, but to be able to switch to powering
the loads off the main panel in case of service needed on the inverters.
The neutrals in this system are all connected together, and I am not sure
if that could cause issues. It is probably difficult to explain all the
details in words, so I am copying part of the three line diagram here. The
second picture is the conductor and conduit schedule.
Tom, I get it that the error sounds like it is on the DC side based on the
words, but when I talked to Midnite about it they were pretty clear about
it being due to multiple N-G bonds and they did not mention that it could
have anything to do with the DC side.
Jason, that is a good idea as well to check the loads that got moved over
to see if there are any other inadvertent N-G bonds on the premises. This
also similar to what Midnite suggested, which was to lift the N-G bond in
the main panel and then see if they are still bonded somewhere else. It
seems like it can be a slow process to track that down with power cut to
the house, but that might be what I have to try if removing the N-G bond in
the solar main disconnect does not help.
So, my main questions to anyone who has an opinion here are two fold:
1. Do you bond the N-G in general in the main solar disconnect for a supply
side connection?
2. Specifically with the Midnite AIO inverters, has anyone else had issues
with this "CA-DC link Overvoltage error" due to having a second N-G bond in
the house? (one in the main service panel, and one in the solar main
disconnect if it is a supply side connection). Or have you seen this error
and found that it was caused by something else?
Cheers,
Dave
On Thu, Oct 23, 2025 at 5:25 PM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> I agree. It is not a separate service. It is a "tap" of the existing
> service (I use that term loosely here). The additional service disconnect
> for the supply side interconnection should have L1, L2, and N
> connected ahead of the premises main disconnect with no EGC. There should
> be a N-G bonding jumper in the PV service disconnect. Then there should be
> no N-G bonds downstream of both the premises main disconnect and the PV
> service disconnect.
>
> Basically, it's the same as two main disconnects running from a meter
> enclosure. Each of the service disconnects has a N-G bond required.
>
> Some AHJs (the crazy ones) require an EGC between the enclosure where the
> supply side connection is made and the PV service disconnect. This creates
> a parallel fault path, and should not be allowed, in my humble opinion.
>
> Now it sounds like you might be doing a partial home backup. The issue
> there is that sometimes the loads or enclosures you moved over the backup
> load panel have inadvertent N-G bonds. Sometimes it's as simple as someone
> who got creative and used a ground as a neutral in a switch box. I say
> simple, but that can be hard to track down.
>
> When Midnite said to remove it from the inverter distribution panel, they
> were probably talking about the protected loads panel.
>
> I think more information is needed.
>
>
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
>
> On Thu, Oct 23, 2025 at 11:03 AM Tyrone Houck via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> My interpretation, and the way it was explained to me by both Ryan
>> Mayfield and Kyle Bolger(several years ago at this point, popular opinion
>> may have changed since). Is that it is not a seperate service.
>> It is however required to have a ground-neutral bond( though in my
>> opinion pointless and redundant as there is a bond in the enclosure where
>> the tap is made). If it gives you any issue, ensure as close to equal
>> potential to the grounding electrode as possible(and make sure your neutral
>> is appropriately sized). I personally don't see the point but it is an NEC
>> requirement
>>
>>
>>
>>
>> On Thu, Oct 23, 2025, 6:08 AM Dave Tedeyan via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Hi All,
>>>
>>> For years I have understood that when doing a supply side connection,
>>> you are supposed to bond the neutral to ground in the solar service
>>> disconnect. I have a Midnite AIO system with two inverters (set up as a
>>> supply side connection) that recently was getting a CA-DC link Overvoltage
>>> error. When talking to Midnite, their first response was to make sure that
>>> there was only one N-G bond in the whole system. When I mentioned that the
>>> solar is a separate service and thus there is a N-G bond in both the main
>>> panel and the inverter distribution panel, they said to remove it from the
>>> inverter distribution panel. I want to make the system work right, but I
>>> also am hesitant to do something against how I have understood the NEC to
>>> be for a long time. I am curious if you all have thoughts on this or run
>>> into a similar situation.
>>>
>>> Cheers,
>>> Dave
>>>
>>> --
>>>
>>> [image: Logo] <https://www.sungineersolar.com/>
>>> Dave Tedeyan, P.E.
>>> Owner | Sungineer Solar
>>> p: he | him | his
>>> a: 1653 Slaterville Rd.
>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>>>
>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>| Ithaca,
>>> NY 14850
>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>>> w: www.sungineersolar.com <http://www.sungineersolar.com/>
>>> c: (607) 270-0370
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20251023/8a4d3ebd/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: PV3.0 as built.jpg
Type: image/jpeg
Size: 2474985 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20251023/8a4d3ebd/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: PV3.1 as built.jpg
Type: image/jpeg
Size: 286875 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20251023/8a4d3ebd/attachment-0003.jpg>
More information about the RE-wrenches
mailing list