[RE-wrenches] Is it OK to add EG4LL-S alongside Fortress e-Vault Classic?
Mick Abraham
mick at abrahamsolar.com
Tue Oct 14 15:18:45 PDT 2025
Hi, Wrenchies~ I sold one E-Vault Classic cabinet to an off-gridder in 2021
(18.5 kWh rated). He set it up open loop even though he's got Schneider XW
Pro. Now he'd like more storage and asked for a quote on one EG4LL-S
cabinet, fully loaded (30.7 kWh).
Surely he would have to stay open loop if these two brands are combined.
Both brands have 16 cells in series = 51.2 nominal volts. However, EG4
documentation calls for 56.2 volts Bulk & Fortress calls for 54.4 volts
Bulk.
War stories or suggestions welcomed; thanks in advance. The Wrench List is
the Bomb!
Mick Abraham, Proprietor
www.abrahamsolar.com
Cell phone or for text messaging: 970-946-6584