It's a regular Cat5/6 Ethernet cable.
Pay attention to termination, though. The Insight Home boxes are internally terminated. So that means it needs to be at the end of the Xanbus chain. The previous models had two RJ45 ports so you could wire the device mid-Xanbus.
Kevin
-----Original Message-----
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Amanda Potter via RE-wrenches
Sent: September-19-25 10:44 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Amanda Potter <adirondackbattery at gmail.com>
Subject: [RE-wrenches] Xanbus Cable question
Hi all,
Is the Schneider “Xanbus” cable a special cable, or just an Cat5/6 Ethernet cable?
Is there a spec for it?
I’m trying to add an “Insight Home” to a XW Pro 6848 & the “Insight Home” does not come with the “Xanbus” cable needed to incorporate it in to the network.
One of my distributors said it’s a plain ole RS485 cable.
Thanks ahead of time!
Amanda Potter
Energy Storage Systems
NABCEP PVIP
Adirondack Battery & Solar, LLC
(315) 212-2114
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
More information about the RE-wrenches
mailing list