[RE-wrenches] Flammable Vapor Ignition Resistant
William Bryce
wlbryce at pineridgeproducts.com
Wed Sep 10 08:27:37 PDT 2025
The C1D2 (Class I, Division 2) rating applies to equipment intended for use
in potentially explosive environments. The PF16 is not suitable for this
type of installation, as it would require a NEMA 4X (or higher) enclosure,
and all conduit and connections would also need to be rated for C1D2
compliance. Additionally, most themselves are not tested for C1D2
environments.
If your AHJ is requiring C1D2-rated equipment, you would need to explore
industrial-rated equipment designed specifically for hazardous locations.
Be aware the battery would come with a increase in cost to meet this
requirement.
I guess you could look at relocating the battery installation outside of
the classified (explosive gas) area. This would allow for the use of
standard equipment without the need for C1D2-rated components.
It may also be helpful for the AHJ to review the UL 9540A test method,
which demonstrates how the battery system behaves under thermal runaway
conditions. This can provide important context for risk assessment and
proper installation practices.
On Wed, Sep 10, 2025 at 5:50 AM Sue Stankevitz via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hi Chris,
>
> To my knowledge the PF batteries do not have a C1D2 rating but that would
> be a question for one of the Midnite Power reps on this page.
>
>
>
> Sue Stankevitz
> MidNite Solar, Inc. <https://www.midnitesolar.com/index.php>
> (360) 403-7207 (XT122)
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Chris Schaefer via RE-wrenches
> *Sent:* Wednesday, September 10, 2025 8:35 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Chris Schaefer <chris at solarandwindfx.com>
> *Subject:* Re: [RE-wrenches] Flammable Vapor Ignition Resistant
>
>
>
> So Sue, where does the MN PowerFlo 16 product stand in regards to class I,
> div II rating?
>
>
>
> Christopher
>
>
>
> On Wed, Sep 10, 2025 at 6:58 AM Sue Stankevitz via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> They may be looking for the Class 1 Div 2 rating with means that it has
> been designed to safely operate in environments where flammable vapors or
> gases exist and have the potential to rise to ignitable concentrations.
> Midnite had to get a charge controller certified to that standard several
> years ago.
>
>
>
> Sue Stankevitz
> MidNite Solar, Inc. <https://www.midnitesolar.com/index.php>
> (360) 403-7207 (XT122)
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jay via RE-wrenches
> *Sent:* Tuesday, September 9, 2025 6:27 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Jay <jay.peltz at gmail.com>
> *Subject:* Re: [RE-wrenches] Flammable Vapor Ignition Resistant
>
>
>
> What would be the rating for that?
>
>
>
> Is it a NEMA or?
>
>
>
> Jay
>
>
>
> On Sep 9, 2025, at 3:08 PM, Glenn via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
>
> Unfortunately codes and standards are constantly changing and inspectors
> are trying to catchup and interpret them as quickly as possible to ensure
> compliance for safety sake.
>
> Erring on the side of safety is their job until educated otherwise
>
>
>
> -Glenn
>
>
>
> On Sep 9, 2025 17:00, Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> That's a first for me. The Enphase battery is sealed, but I don't know if
> that qualifies as sealed against vapor.
>
>
>
> I'd reach out to Enphase to get some guidance on that. It's always
> something with these AHJs.
>
>
> Jason Szumlanski
>
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
>
> Florida Certified Electrical Contractor EC13013208
>
>
>
>
>
> On Tue, Sep 9, 2025 at 4:13 PM Zeke Yewdall via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> My interpretation of this is that he wants to make sure that the battery
> cannot ignite a flammable vapor cloud from gasoline being spilled in
> the garage. If he's saying that no electrical equipment that might create
> a spark (such as with a relay or switch or circuit breaker) can be below
> 18", that may be the case. I might be completely off base here, but I
> don't think it has anything to do with it being a battery really, but just
> a piece of electrical equipment that might have relays or sparking things
> inside? Maybe? In which case... does the 5p have any relays or
> contactors, or is it's BMS all solid state? And second question would be
> can you document that.
>
>
>
> Zeke
>
>
>
> ---------------------------------
>
> Seeking your suggestions and direction. My AHJ - after acknowledging that
> the Enphase 5p battery has a floor mount option - now insists that it must
> be 18-inches above the garage floor unless I can produce something that
> says it is "Flammable Vapor Ignition Resistant."
>
> We all know there is no open flame from an ESS and I know the 9540A
> depicts a battery at 6-inches.
>
> Anybody run into this and have suggestions on what I might show back to
> the AHJ?
>
> Howard "Scot" Arey
> Owner, Solar CenTex
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
>
> --
>
> Chris Schaefer’s
> [image: Image removed by sender.]
>
> *Tel 585-229-2083 or Cell 585-748-1870 *
> *5115 S Hill Road ~ Canandaigua New York 14424 www.solarandwindfx.com
> <http://www.solarandwindfx.com> ~ E-mail: **chris at solarandwindfx.com
> <chris at solarandwindfx.com>*
>
> *[image: Image removed by sender.]*
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250910/8e5214e8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ~WRD0000.jpg
Type: image/jpeg
Size: 823 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250910/8e5214e8/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 4417 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250910/8e5214e8/attachment.gif>
More information about the RE-wrenches
mailing list