[RE-wrenches] ESS and Calculated Load in Texas
Jason Szumlanski
jason at floridasolardesigngroup.com
Mon Aug 4 13:01:03 PDT 2025
I have heard this as well. My situation was specific to NEC 2020, and I
have not studied 2023 in detail. We have 17 months left before switching
here.
It's going to come down to what automatically managing the load means. If
the microgrid shuts down when the load is too high, there you go - it was
"managed." When the load decreases, it starts back up. Just call the entire
load a "smart load."
Confusing for sure. And quite ridiculous, frankly.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Mon, Aug 4, 2025 at 1:47 PM August Goers <august at luminalt.com> wrote:
> Hi Chris -
>
> I've attended a few meetings over the last couple of years discussing this
> point in preparation for adoption of the 2023 NEC in CA (which is going to
> be January 2026) - of course there are jurisdictions that have already
> adopted the 2023 NEC, and it sounds like you're in one of them. Here are
> some notes:
>
>
> 1. 2023 NEC 710.1 removes ESS that operate both connected to the grid
> and in island mode from the scope. The intended section that applies to
> grid connected ESS with a MID is 702 Optional Standby Systems. I think that
> Jason's argument for following 710 is good, but my understanding from
> several experts is that the actual NEC intention is for us to follow 702.
> 2. 2023 702.4(A)(2)(b) allows systems with Energy Management Systems
> (EMS) "that will automatically manage the connected load" to "have a
> capacity sufficient to supply the maximum load that will be connected by
> the EMS." This would allow the largest load method that we have been used
> to, as long as there is an EMS that will either shed loads or manage the
> system to alert the owner to reduce loads.
> 3. Some equipment might have the UL 916 Energy Management Equipment
> listing which you could point out to the AHJ. Other equipment might have
> load control capability.
>
> The 2026 NEC 702 Optional Standby Systems draft is as seen here and has a
> new multimode inverter based system section:
>
> [image: image.png]
>
> It's definitely confusing!
>
> August
>
>
>
>
> On Sat, Aug 2, 2025 at 11:18 AM Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> We are still on NEC 2020, but I had this issue with a jurisdiction here
>> recently, and I am just going to cut and paste my winning argument here for
>> your benefit. Take from it whatever you think might help. My permit was
>> issued less than an hour after sending this.
>>
>> --------
>>
>> Dear [Insert Misinformed Plan Reviewer Name Here],
>>
>> I think you are still misinterpreting the scope of Article 702. This is a
>> common issue that was cleared up in the 2023 language, where they removed
>> the phrase you are referring to after it caused mass confusion in the 2020
>> version. Here is why Article 702 does not apply (and others do):
>>
>> *(all bold, italic, and underlined emphasis below is added by me)*
>>
>> The system we are installing is connected in parallel with the utility
>> source, which is covered by Article 705, *Interconnected *Electric Power
>> Production Sources. Section 705.2 defines a Microgrid-Interconnect Device,
>> which in this case is the Enphase System Controller. If you look at the
>> last paragraph of Section 705.40, Loss of Primary Source, an interconnected
>> source is permitted to operate in *island mode* when the primary source
>> is lost. Head over to Section 710.1 where the scope for Stand-alone Systems
>> is defined. This is the Article where island mode is discussed. That is why
>> the governing section for this installation with respect to loads is
>> 710.15(A), which allows for an *islanded* system to have less capacity
>> than the calculated load.
>>
>> Article 702 does not apply here as that covers standby systems, and this
>> is not a standby system. This is an islandable interconnected power source.
>> A standby system is one that does not function in an interactive manner
>> with the utility grid. The reason storage batteries were added to this
>> section is that you *can* have storage batteries that are *not* capable
>> of interacting with the utility grid, but *do* supply standby power, as
>> is the case of an Uninterruptible Power Supply (UPS). This would also be
>> the case if you have batteries with a multimode inverter with an integrated
>> transfer switch that disconnects from the grid during an outage to supply
>> selected loads, but does not "sell" power to the grid. That type of backup
>> system *would* need to comply with Article 702 because it is not an
>> interconnected power source. It is simply a load with respect to the
>> primary power source (utility).
>>
>> By the way, side note... Enphase also offers a Sunlight Backup Only
>> system, which uses microinverters with the same System Controller, but no
>> battery whatsoever. It only provides power during the day to the extent
>> that there is enough solar irradiance available to loads. This is a perfect
>> example of why Article 710 rules in the case of an islanded interconnected
>> system. It is not a standby system. The solar power supply is variable,
>> necessitating the system to function at a capacity that is less than the
>> connected load. A microgrid is a very different system than a standby
>> system. A microgrid can be comprised of various sources of power, which can
>> include utility, batteries, solar, generators, and others. The major
>> distinction between Articles 705 and 702 is the Microgrid Interconnect
>> Device. Article 702 relies upon a transfer mechanism with no interactive
>> component.
>>
>> I hope that clears it up. We code nerds in the industry saw this coming,
>> but it is pretty clear once you make the distinction between an islanded
>> interactive system versus a standby system.
>>
>> Article 710 is small, but mighty!
>>
>> --------------
>>
>>
>>
>>
>>
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>> On Sat, Aug 2, 2025 at 1:56 PM Chris Sparadeo via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Hi all,
>>>
>>> I’m finding out that some jurisdictions in Texas are requiring ESS
>>> output to be equal to or greater than the calculated load of a dwelling.
>>> For example, if backing up the whole home, and the service load is
>>> calculated at 150A, the ESS would require to continuously output 150A OR
>>> EMS is required to bring the calculated load to or below that of the ESS.
>>> AHJ’s in a few areas of Texas are dying on this hill and to actually meet
>>> the calculated load, systems would need to be significantly larger than
>>> needed.
>>>
>>> I know that previous versions of 706 (specifically NEC 2017) could lead
>>> one to argue this point, but Texas had adopted NEC 2023, and it’s only
>>> article 710 that indicates a system operating in isolation of the grid
>>> should has sufficient output to supply load to the largest backed up load.
>>>
>>> Has anyone run into this issue? And if so, what have people been doing
>>> to either meet these outdated requirements or successfully push back?
>>>
>>> Thanks!
>>>
>>>
>>> Chris Sparadeo
>>>
>>> VT Master Electrician # EM 08220
>>> C_802-369-4458
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250804/1b9a765e/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 193027 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250804/1b9a765e/attachment-0001.png>
More information about the RE-wrenches
mailing list