[RE-wrenches] Battery RSD
Christopher Warfel
cwarfel at entech-engineering.com
Thu Jul 31 03:39:44 PDT 2025
Good work all, and to Mr. Nelson for pursuing. I am in the middle of
two battery designs, and I am hoping our inspector doesn't make the same
mistake. Now I can show this thread if so. Chris
On 7/30/2025 3:58 PM, MDElectricSolar via RE-wrenches wrote:
> Yes! Thanks to all of the amazing wrenches who continually share their
> vast knowledge and experiences.
>
> Michael D Nelson
> MD Electric & Solar, Inc.
> 707-684-0064 mobile
> 707-884-1862 office
> www.mdelectricsolar.com
> www.facebook.com/mdelectricandsolar
>
>
>> On Jul 30, 2025, at 12:47 PM, Jason Szumlanski via RE-wrenches
>> <re-wrenches at lists.re-wrenches.org> wrote:
>>
>>
>> Whew! That is a relief. Good for you for taking it to the next level.
>> These inspectors can't keep claiming that the "industry is new." They
>> need to get with the times!
>>
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>> On Wed, Jul 30, 2025 at 3:33 PM MDElectricSolar
>> <mdelectricsolar at gmail.com> wrote:
>>
>> I emailed and eventually spoke with the building inspector
>> supervisor and got him to agree that what they're looking for is
>> an AC disconnect, within sight of the ESS which disconnects and
>> locks open any connection to the house. He was going to reiterate
>> to his inspectors that it is not between the battery and the
>> inverter.
>> Michael D Nelson
>> MD Electric & Solar, Inc.
>> 707-684-0064 mobile
>> 707-884-1862 office
>> www.mdelectricsolar.com <http://www.mdelectricsolar.com>
>> www.facebook.com/mdelectricandsolar
>> <http://www.facebook.com/mdelectricandsolar>
>>
>>
>>> On Jul 30, 2025, at 12:21 PM, Jason Szumlanski via RE-wrenches
>>> <re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>
>>> True, but a suitable DC rated disconnect switch with large
>>> enough terminals is going to be very expensive.
>>>
>>> The whole thing boils down to the definition of an ESS. Getting
>>> the inspector to realize that the 706.2 disconnect is not
>>> required to be a*battery* disconnect is key here.
>>>
>>>
>>> Jason Szumlanski
>>> Principal Solar Designer | Florida Solar Design Group
>>> NABCEP Certified Solar Professional (PVIP)
>>> Florida State Certified Solar Contractor CVC56956
>>> Florida Certified Electrical Contractor EC13013208
>>>
>>>
>>> On Tue, Jul 29, 2025 at 11:38 PM William Miller via RE-wrenches
>>> <re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>> Jason:
>>>
>>> Fine stranded cables can be used with set screw terminals if
>>> you use ferrules.
>>>
>>> You hint at a broader point: The industry is not providing
>>> solutions that the regulators are demanding. Any battery
>>> with BMS should have a remote inhibit. Problem solved.
>>>
>>> William
>>>
>>> Miller Solar
>>>
>>> 17395 Oak Road, Atascadero, CA 93422
>>>
>>> 805-438-5600
>>>
>>> www.millersolar.com <http://www.millersolar.com/>
>>>
>>> CA Lic. 773985
>>>
>>> *From:*RE-wrenches
>>> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
>>> Behalf Of *Jason Szumlanski via RE-wrenches
>>> *Sent:* Tuesday, July 29, 2025 2:45 PM
>>> *To:* RE-wrenches
>>> *Cc:* Jason Szumlanski
>>> *Subject:* Re: [RE-wrenches] Battery RSD
>>>
>>> The problem I see with just complying is that there is
>>> really no practical or cost-effective way to comply. You
>>> would have to somehow transition from battery cable to some
>>> other cable type, because typical fusible disconnect switch
>>> lugs are not going to be rated to accept
>>> fine-stranded battery cable, especially in the required size.
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't
>>> work, try the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't
>>> work, try the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try
>> the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
--
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401) 447-5773
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250731/9d9349e1/attachment.htm>
More information about the RE-wrenches
mailing list