[RE-wrenches] Battery RSD
MD Electric & Solar
mdelectricsolar at gmail.com
Tue Jul 29 10:14:34 PDT 2025
I would normally want at least a 200A rated DC disconnect, as William
discusses above, but the inspector said a 100A knife switch would satisfy
him, just as an emergency kill switch. I would love to see the battery
manu's have an internal kill switch with a small RSD button that we could
locate next to the other required RSD button.
William, there is no lockable feature on the simpliphi/briggs LFP
batteries, unfortunately.
On Tue, Jul 29, 2025 at 10:09 AM Sue Stankevitz <Sue at midnitesolar.com>
wrote:
> Midnite does not offer an outdoor rated enclosure for our large breakers
> but if only 100a was needed as Mike was asking about our MNPV3 with an
> MNEPV100(100a DC breaker) would be outdoor rated and lockable.
>
>
>
> Sue Stankevitz
> MidNite Solar, Inc. <https://www.midnitesolar.com/index.php>
> (360) 403-7207 (XT122)
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *MD Electric & Solar via RE-wrenches
> *Sent:* Tuesday, July 29, 2025 12:46 PM
> *To:* jay <jay.peltz at gmail.com>
> *Cc:* MD Electric & Solar <mdelectricsolar at gmail.com>; RE-wrenches <
> re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] Battery RSD
>
>
>
> Wondering if Midnight solar makes something outdoor rated, with a typical
> 250ADC breaker, like this:
>
> Outdoor rated, lockable....
>
>
> https://www.midnitesolar.com/productPhoto.php?product_ID=76&productCat_ID=8&sortOrder=5&act=p
>
>
>
> On Tue, Jul 29, 2025 at 9:39 AM jay <jay.peltz at gmail.com> wrote:
>
> Maybe if you left the key on a chain to open the door, and placard with
> instructions on the outside that would work?
>
>
>
>
>
> On Jul 29, 2025, at 10:23 AM, MD Electric & Solar <
> mdelectricsolar at gmail.com> wrote:
>
>
>
> Correct, it does not have an external disconnect, but if you open the
> cover, each battery has it's own disconnect and the Sol-Ark has a battery
> disconnect.
>
> Looks like I'm in the market for a 100 amp rated outdoor, lockable DC
> rated knife switch.
>
> Mike
>
>
>
> On Tue, Jul 29, 2025 at 9:16 AM jay <jay.peltz at gmail.com> wrote:
>
> I had to look up that battery enclosure and if I understand correctly it
> does not have an external breaker/disconnect so yes the inspector is
> correct in the need for one if I understand.
>
>
>
> jay
>
>
>
>
>
>
>
>
>
>
>
> On Jul 29, 2025, at 10:09 AM, MD Electric & Solar <
> mdelectricsolar at gmail.com> wrote:
>
>
>
> Here is the reference, attached.
>
>
>
> On Tue, Jul 29, 2025 at 8:49 AM jay <jay.peltz at gmail.com> wrote:
>
> I’ll let the code experts chime in, but I would ask for the code reference
> they are referring to.
>
> The only one I can think of has to do with if the batteries are on the
> other side of a wall.
>
> Thats as clean an install as they come
>
> jay
>
>
>
> > On Jul 29, 2025, at 9:43 AM, MDElectricSolar <mdelectricsolar at gmail.com>
> wrote:
> >
> > <image0.jpeg>
> > Michael D Nelson
> > MD Electric & Solar, Inc.
> > 707-684-0064 mobile
> > 707-884-1862 office
> > www.mdelectricsolar.com
> > www.facebook.com/mdelectricandsolar
> >
> >
> >> On Jul 29, 2025, at 8:06 AM, Jay via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
> >>
> >> What is the layout of the equipment
> >>
> >> Are the batteries next to and therefore in sight of the inverter?
> >>
> >> Jay
> >>
> >>> On Jul 29, 2025, at 8:44 AM, MDElectricSolar via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
> >>>
> >>> Wrenches,
> >>> I have a building inspector in my county of Sonoma who has just told
> me that we need to install a rapid shutdown switch of some type between my
> LFZ battery bank and my Solark 15k inverter. He mentioned some type of
> knife switch within 5 feet of the equipment. I cannot find any reference to
> this requirement anywhere but he insists it is required. These batteries
> happen to be simplify or brakes and Stratton batteries and each battery has
> its own 80 amp breaker on the battery and the Solark has a battery
> disconnect switch built-in. We do have module level RSD which kills the
> solar output as well as the inverter output when the button is pushed. Does
> anyone have any experience with this or can they point me to the correct
> code section or what are others doing to comply with this requirement?
> >>>
> >>>
> >>> Michael D Nelson
> >>> MD Electric & Solar, Inc.
> >>> 707-684-0064 mobile
> >>> 707-884-1862 office
> >>> www.mdelectricsolar.com
> >>> www.facebook.com/mdelectricandsolar
> >>>
> >>> _______________________________________________
> >>> List sponsored by Redwood Alliance
> >>>
> >>> Pay optional member dues here: http://re-wrenches.org
> >>>
> >>> List Address: RE-wrenches at lists.re-wrenches.org
> >>>
> >>> Change listserver email address & settings:
> >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>>
> >>> There are two list archives for searching. When one doesn't work, try
> the other:
> >>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> >>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>>
> >>> List rules & etiquette:
> >>> http://www.re-wrenches.org/etiquette.htm
> >>>
> >>> Check out or update participant bios:
> >>> http://www.members.re-wrenches.org
> >>>
> >> _______________________________________________
> >> List sponsored by Redwood Alliance
> >>
> >> Pay optional member dues here: http://re-wrenches.org
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Change listserver email address & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> There are two list archives for searching. When one doesn't work, try
> the other:
> >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> http://www.re-wrenches.org/etiquette.htm
> >>
> >> Check out or update participant bios:
> >> http://www.members.re-wrenches.org
> >>
>
>
>
>
> --
>
> Michael D Nelson
>
> MD Electric & Solar Inc.
>
> Office: 707-412-3181
>
> Cell: 707-684-0064
>
> www.mdelectricsolar.com
>
> www.facebook.com/mdelectricandsolar
>
>
>
>
>
> <PRMD BLD_20250728_062230.pdf>
>
>
>
>
>
>
> --
>
> Michael D Nelson
>
> MD Electric & Solar Inc.
>
> Office: 707-412-3181
>
> Cell: 707-684-0064
>
> www.mdelectricsolar.com
>
> www.facebook.com/mdelectricandsolar
>
>
>
>
>
>
>
>
>
>
> --
>
> Michael D Nelson
>
> MD Electric & Solar Inc.
>
> Office: 707-412-3181
>
> Cell: 707-684-0064
>
> www.mdelectricsolar.com
>
> www.facebook.com/mdelectricandsolar
>
>
>
>
>
--
Michael D Nelson
MD Electric & Solar Inc.
Office: 707-412-3181
Cell: 707-684-0064
www.mdelectricsolar.com
www.facebook.com/mdelectricandsolar
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250729/0156011e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 4417 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250729/0156011e/attachment.gif>
More information about the RE-wrenches
mailing list