[RE-wrenches] Paralleling two PF16 batteries on Midnite AIO
Ray Walters
ray at solarray.com
Thu Jul 17 16:10:08 PDT 2025
I was told specifically by Midnite Tech support that the AIO was
designed for parallel conductors. There isn't anything in the manual
that contradicts that, that I'm aware of.
I have never considered 2 lugs on a single bolt a violation. Its when
two conductors go into a single lug that is not designed for 2
conductors, that it's considered double lugging. If 2 lugs on one bolt
were not legal, how in the world would you ever wire L16s, golf cart
batteries, etc. in parallel?
Ray Walters
Remote Solar
On 7/17/2025 3:50 PM, Jason Szumlanski via RE-wrenches wrote:
> This is an interesting option. I think it goes against the manual,
> however, which could be flagged as a code violation.
>
> I also considered Polaris taps that are rated for fine-stranded wire.
>
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
>
> On Thu, Jul 17, 2025 at 11:41 AM Zeke Yewdall via RE-wrenches
> <re-wrenches at lists.re-wrenches.org
> <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>
> I have done several systems where we just paralleled two
> batteries on the battery terminals, just like we'd do with lead
> acid batteries, with a reverse return for the home runs. With the
> active balancing, the reverse return is apparently not as
> important, but I still think it's best practice.
>
> MidNite Power is working on a custom gutter/wiring box for
> coupling the PF16's directly to the AIO, but not sure on timeline
> for it. I've seen a few really nice installs where someone used a
> standard 10" gutter with cutouts in it directly on top of the
> PF16's, then set the AIO's on top of that. No exposed wiring or
> even conduit showing.
>
> Zeke
> --
> Zeke Yewdall
> PV Engineer
> NABCEP #031508-89
> zeke at darkforestsolar.com
> 303-523-3592
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> There are two list archives for searching. When one doesn't work,
> try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <http://www.members.re-wrenches.org>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250717/bab636d5/attachment.htm>
More information about the RE-wrenches
mailing list