[RE-wrenches] 500V "Crowbar"
    jay 
    jay.peltz at gmail.com
       
    Mon Jun 16 15:15:49 PDT 2025
    
    
  
The LUX powered 12kw has a 600vdc input with 25 amp limitation on PV 1
Which fits your specifications perfectly.
You can get them under the fortress or EG4 name
jay
> On Jun 16, 2025, at 2:41 PM, Travis Knipple via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Hi all,
> 
> This is a repeated (rephrased) version of a previous question, but I've hit upon a new application.
> I'm looking to retrofit a system from existing SMA Sunny Boy inverters to work with an ESS System.
> My PV Array (~900' from the inverters) is 600V Voc, and the strings are combined at the Array, so Imp is 24A, Isc is 32A.
> Also, important to note is that 1 of my SB7000 inverters is non functional.
> 
> So, my options are:
> (A) A 500V "Crowbar" or SRC type circuit to limit my Voc, and allow me to take the array directly to a single MPPT port on a Sol-ark Inverter
> Or, use AC-Coupling to the Sol-Ark, then I can...
> (B) A new PV Inverter that can handle 600V, 32A (Isc) on a single MPPT Port
> (C) A replacement SB7000
> (D) Re-pull my strings of wires to something like a Solis PV Inverter
> 
> Does anyone know of either:
> (A) a Voc limiter?
> (B) A PV Inverter with a single MPPT input that can handle 600V, 24A (Imp), 32A (Isc)
> or 
> (C) A source for a replacement SB7000US
> 
> --
> Travis Knipple
> Senior Engineer
> Hudson Solar Solutions LLC
> Rhinebeck, NY 12572
> 518-539-8040 x408 | travis at hudsonsolarsolutions.com <mailto:travis at hudsonsolarsolutions.com>
> 
> 
> PVIP# PV-111821-013612
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250616/95674ed3/attachment.htm>
    
    
More information about the RE-wrenches
mailing list