I just can't believe that Midnite would not have solar stay on after 
LBCO !
Schneider and Outback always did this from a long way back to Trace.

Hear the water sound as it circles the drain?

Dave Angelini Offgrid Solar
"we go where powerlines don't"
    [1]https://offgridsolar1.com/ [2]  [1]
e-mail  offgridsolar at sti.net
text 209 813 0060

On 2025-05-12 10:33 am, MDElectricSolar via RE-wrenches wrote:

> We have been using the Solark inverter for GTBB and off grid clients. 
> In the case of low battery cut out the solar does stay alive in the 
> background and will recharge the batteries when the sun comes out the 
> next day and turn itself back on and provide AC power output.
> 
> Michael D Nelson
> MD Electric & Solar, Inc.
> 707-684-0064 mobile
> 707-884-1862 office
> www.mdelectricsolar.com
> www.facebook.com/mdelectricandsolar
> 
>> On May 12, 2025, at 10:13 AM, Ray Walters via RE-wrenches 
>> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> So the bypass switch gets the house power on, and I too always 
> recommend a hard bypass switch. However, you still need a 48 v power 
> supply to get the battery system back up, and that's becoming a serious 
> pain in my aging backside.  Until AIOs with Li+ batteries, lead acid 
> would have enough voltage to get the charge controller to come back on, 
> and eventually the customer could get the inverter back on too.  No 
> special trip out.
> 
> We need an independent circuit that would sense array voltage, and wake 
> up the battery, so it could take a charge: a backup battery for the 
> offgrid battery.  Without that, AIOs and Li+ batteries are not self 
> healing like Lead Acid.  We are going backwards fast, but with an 
> amazing amount of new Chinese technology driving the jalopy in reverse. 
>  (Danger Will Robinson)
> 
> Ray Walters
> Remote Solar
> 
> On 5/12/2025 10:54 AM, Jason Szumlanski via RE-wrenches wrote:
> 
> We always recommend a transfer switch to bypass the inverter and send 
> generator power to the loads. Most clients take us up on it. For 
> retrofits, sometimes there can be space limitations, however.
> 
> As for the function of the AIO, there is no integrated mechanical 
> bypass, and since there is an internal relay controlling the generator 
> input (or smart load output on that breaker), I think the default 
> function is for the relay to open when the inverter turns off. AC 
> voltage on the load side of the breaker does not close the relay and 
> turn the inverter back on automatically.
> 
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
> 
> On Mon, May 12, 2025 at 9:49 AM Dave Angelini Offgrid Solar via 
> RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
> All sounds wrong to me. Call Midnite.
> 
> Typically there is a AC bypass mechanical switch that allows the gen to 
> bypass the inverter and power loads.
> 
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> [1]https://offgridsolar1.com/ [2]  [1]
> e-mail  offgridsolar at sti.net
> text 209 813 0060
> 
> On 2025-05-12 9:29 am, Jason Szumlanski via RE-wrenches wrote:
> 
> Maybe I'm missing something, but it seems like there is a flaw in the 
> logic for how generator integration works with this product. Unlike 
> some of the other AIOs, you can't put the generator on the Grid input 
> in an off-grid scenario. You have to use the Generator smart load 
> breaker, which isn't a dedicated generator input, but a programmable 
> circuit. This is problematic because it seemingly has a normally open 
> internal relay that closes only when the inverter is ON. At least, 
> that's how it seems to work in my limited experience.
> 
> Why is this a problem? If the battery capacity drops below the low 
> voltage cutoff, the inverter turns off. You have to turn the inverter 
> ON for the generator relay to close so you can charge the battery, but 
> since the battery is too low, the inverter won't turn on. You would 
> have to reprogram the inverter to drop the cutoff voltage/SOC below the 
> current battery state. For people who do not want to use AGS, or if AGS 
> fails to start the generator for any reason, getting the generator to 
> charge the battery manually is no easy task.
> 
> Moreover, turning the generator on manually when the inverter is in an 
> OFF state will not pass power to the loads, and will not turn the 
> inverter ON automatically. You have to get the inverter turned ON 
> somehow so that the generator power can pass through to the loads. And 
> since the startup sequence for this inverter is very quirky, 
> non-intuitive, and unreliable, that makes the problem even worse. I'm 
> not sure if you can even turn the inverter ON when there is generator 
> input and the battery is too low. I don't think you can because the 
> relay is open and the inverter doesn't even see generator voltage when 
> it is in an OFF state.
> 
> This seems like a serious oversight and a reason to go with one of the 
> other AIOs on the market. I believe the Sol-Ark 15K and EG4 18kPV will 
> both immediately power loads and start charging when the generator is 
> on, regardless of whether the generator is connected to the Grid or 
> Generator input. Any AC input immediately passes through to the loads. 
> This is because those inverters stay "on" when a low battery condition 
> is met, and they simply stop using the battery to invert power if the 
> battery conditions do not allow it, based on the settings.
> 
> The logic of the Midnite AIOs turning "off" when battery cutoff is met 
> and opening the generator relay doesn't make sense to me. Am I wrong 
> about how this works?
> 
> Jason Szumlanski
> Principal Solar Designer
> Florida Solar Design Group
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

  _______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
------
[1] http://members.sti.net/offgridsolar/
[2] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250512/fd3dc3fe/attachment.htm>


More information about the RE-wrenches mailing list