[RE-wrenches] Midnite AIO Generator Functionality
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Mon May 12 09:46:34 PDT 2025
All sounds wrong to me. Call Outback.
Typically there is a AC bypass mechanical switch that allows the gen to
bypass the inverter and power loads.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridsolar at sti.net
text 209 813 0060
On 2025-05-12 9:29 am, Jason Szumlanski via RE-wrenches wrote:
> Maybe I'm missing something, but it seems like there is a flaw in the
> logic for how generator integration works with this product. Unlike
> some of the other AIOs, you can't put the generator on the Grid input
> in an off-grid scenario. You have to use the Generator smart load
> breaker, which isn't a dedicated generator input, but a programmable
> circuit. This is problematic because it seemingly has a normally open
> internal relay that closes only when the inverter is ON. At least,
> that's how it seems to work in my limited experience.
>
> Why is this a problem? If the battery capacity drops below the low
> voltage cutoff, the inverter turns off. You have to turn the inverter
> ON for the generator relay to close so you can charge the battery, but
> since the battery is too low, the inverter won't turn on. You would
> have to reprogram the inverter to drop the cutoff voltage/SOC below the
> current battery state. For people who do not want to use AGS, or if AGS
> fails to start the generator for any reason, getting the generator to
> charge the battery manually is no easy task.
>
> Moreover, turning the generator on manually when the inverter is in an
> OFF state will not pass power to the loads, and will not turn the
> inverter ON automatically. You have to get the inverter turned ON
> somehow so that the generator power can pass through to the loads. And
> since the startup sequence for this inverter is very quirky,
> non-intuitive, and unreliable, that makes the problem even worse. I'm
> not sure if you can even turn the inverter ON when there is generator
> input and the battery is too low. I don't think you can because the
> relay is open and the inverter doesn't even see generator voltage when
> it is in an OFF state.
>
> This seems like a serious oversight and a reason to go with one of the
> other AIOs on the market. I believe the Sol-Ark 15K and EG4 18kPV will
> both immediately power loads and start charging when the generator is
> on, regardless of whether the generator is connected to the Grid or
> Generator input. Any AC input immediately passes through to the loads.
> This is because those inverters stay "on" when a low battery condition
> is met, and they simply stop using the battery to invert power if the
> battery conditions do not allow it, based on the settings.
>
> The logic of the Midnite AIOs turning "off" when battery cutoff is met
> and opening the generator relay doesn't make sense to me. Am I wrong
> about how this works?
>
> Jason Szumlanski
> Principal Solar Designer
> Florida Solar Design Group
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
Links:
------
[1] http://members.sti.net/offgridsolar/
[2] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250512/3150ae2a/attachment.htm>
More information about the RE-wrenches
mailing list