Is inverter 2 on top?  The top inverter in an Outback dual stack always 
runs hotter, because the heat from the bottom inverter is adding to its 
own heat.  I used to see that consistently cause board failures on the 
top inverter more often, if the whole system was running close to capacity.

Ray Walters

On 5/12/2025 7:56 AM, Amos Post via RE-wrenches wrote:
> UPDATE:
>
> So far so good and since replacing the fuse holder, fuse #3 has not 
> blown again.
>
> ANOTHER ISSUE:
>
> *Inverter 2 runs hotter than inverter 1.*   Reminder this is grid-tied 
> system with 2-GVFX3648’s in series for 120/240V.   The fan on inverter 
> #2 had malfunctioned, but I was able to replace it and get that going 
> again.  Even with the replaced fan, inverter #2 is still running 
> noticeably hotter.  My understanding is that both inverters in this 
> system are essentially “Masters”, since this is grid-tied.  Shouldn’t 
> the load/generation be split between the two and hence they run 
> equally as hot?  I did check the stacking and they were both set to 
> “Master” which is I think what they recommended for grid-tie.  I tried 
> switching the ports on the Hub that they are plugged into to see if 
> that would change anything, but no change.  I did also noticed while I 
> was there last week that while both inverters had the solid yellow “AC 
> IN” light on, inverter #2’s green “Inverter” light was always on, 
> while inverter #1’s green “Inverter” seemed to come and go…
>
> Any ideas?
>
> Thanks as always,
> Amos
>
>
>
>
>
>
>
>        Amos Post
> Integrity Energy
>   W 802.763.7023
>    C 802.291.2188
> ienergyVT.com <http://www.ienergyvt.com>
> Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>
>> On Apr 15, 2025, at 8:40 AM, Amos Post <integrityenergy101 at gmail.com> 
>> wrote:
>>
>> Hi all,
>>
>> I decided to start with the simple stuff.  While I don’t have a 
>> string curve tester (I should have one), yesterday I tested strings 
>> 1,2,3 individually under load.  String 3 is the one that’s been 
>> blowing the fuse.  I did not test strings 4-6 which are on a separate 
>> charge controller and combiner.  Here are the results:
>>
>> String 1- 7.1A at 76V
>> String 2- 7.77Aat 79V
>> String 3-7.13A at 78.3V
>>
>> I did notice that the second charge controller with strings 4-6 was 
>> running about 100watts more (1800w vs 1700w).  The conditions were 
>> clear blue skies.  I replaced the fuse holder and fuse.  If it blows 
>> again I’ll try switching strings to see if it follows…
>>
>> Thanks for your feedback and I’ll keep ya’ll posted.
>>
>> Amos
>>
>>
>> <IE LOGO 150x78.jpg>
>>
>>        Amos Post
>> Integrity Energy
>>   W 802.763.7023
>>    C 802.291.2188
>> ienergyVT.com <http://www.ienergyvt.com/>
>> Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>>
>>> On Apr 11, 2025, at 4:07 PM, Jerry Shafer via RE-wrenches 
>>> <re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>> Wrenches, Amos, blowing of a 15 amp fuse is not a ghost in the 
>>> machine, it is an actual issue no way around it, shorted modules, 
>>> shorted diodes, in most cases it's a home run, way back when USE-2 
>>> white wure was failing and would crack and break off mostly this 
>>> would result in a GFI trip. The fuse is blowing because of over 
>>> current and a single string of your vintage will max out at far less 
>>> than 10 amps but the other two strings will back feed this fuse with 
>>> close to 20 then pop.
>>> Sharp had module failures resulting in cell shorts, look very close 
>>> there. I have inspected arrays with extreme exposure differences, 
>>> this will effect performance but should not pop a fuse. Do you have 
>>> a module string curve tester, this very well may show an issue of 
>>> the string but eyes on the array is required to located the cause.
>>> I have seen nails through wires, conduit, racking in contact with 
>>> the back of the module but this will trip the GFI breaker not the 
>>> string fuse.
>>> Fun times.
>>>
>>>
>>> On Fri, Apr 11, 2025, 12:49 PM david quattro via RE-wrenches 
>>> <re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>     One time I had similar, but different problem:  1 Amp ground
>>>     fault fuse consistently blowing, sometimes after 1 day sometimes
>>>     after weeks/months.  I tried everything - replaced home runs,
>>>     checked VOC, VMP, swapped DC input into a different inverter,
>>>     etc. it kept coming back to this one string. I checked every
>>>     module VOC, ISC, every connection, no pinched wires, no
>>>     discernible problem, but fuse blowing.
>>>        Luckily it was a medium size commercial job (on a fire
>>>     station) so I was able to scatter all the modules of this
>>>     suspect string all over the roof, and carefully track where I
>>>     had put them. That’s when the problem went away and never came
>>>     back..😂
>>>       Best I could figure was a slight manufacturing error that had
>>>     a compounding/cumulative effect. So once I got those consecutive
>>>     serial numbers away from each other no more problem. Either that
>>>     or the fire chief was fucking with me and he was burning out the
>>>     fuses, which I doubt
>>>
>>>
>>>
>>>     On Fri, Apr 11, 2025 at 8:05 AM Mac Lewis via RE-wrenches
>>>     <re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>         Hello Amos,
>>>
>>>         Have you checked for voltage imbalance for each string?  If
>>>         you have a bad diode, that string may run low on voltage and
>>>         be trying to send current toward the weak string (this is
>>>         the reason you have these breakers).  I'd run each string
>>>         independently and see what Vmp is.  If you are missing some
>>>         voltage that may be a clue.  You can also independently
>>>         clamp each string during operation.
>>>
>>>         I like IR cameras for this type of thing.  It may just be a
>>>         bad connection, heat build up, fuse holder issue.
>>>
>>>         Let us know what you find out
>>>
>>>         On Fri, Apr 11, 2025 at 8:07 AM Amos Post via RE-wrenches
>>>         <re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>             Hi Wrenches,
>>>
>>>             I have a bit of a puzzler that I’m trying to get sorted
>>>             out.  I’ve been servicing a Grid-Tied Battery Backup
>>>             system that’s about 17-18 years old.  The system
>>>             comprises of 2-GVFX3648s in series, with 2-MX60(at least
>>>             I think they are 60s) CC’s. Each CC has 3 strings of 3
>>>             tied to it, and each string has a 15A in-line 600V fuse.
>>>             The modules are I believe are like 230/240Watt 60 cell
>>>             modules (sorry I don’t have pictures/specifics).   We
>>>             replaced the flooded batteries with AGMs about a year
>>>             and a half ago.
>>>
>>>             The situation is one of the 15A string fuses keeps
>>>             blowing.  It’s now happened 3 times and its the same
>>>             fuse every time.  First we just replaced the fuse and
>>>             under the surge/lightning assumption.  Fuse blew again.
>>>             Then I thought I found the culprit.  The #6 PV output
>>>             from the combiner to the PV input breaker for the CC was
>>>             a bit darkened and very warm to the touch when I
>>>             replaced the fuse the first time.   So I though maybe it
>>>             was a loose connection on that lug and that caused
>>>             everything to heat up and eventually blow the fuse.  I
>>>             cut and stripped the wire back and cleaned the lug and
>>>             re-seated the wire in the lug.  Fuse blew again within a
>>>             few months time.  I then checked the Junction box on the
>>>             roof where the USE-2 wire connects to THHN, and did a
>>>             visual inspection of all the wiring on the roof.  All of
>>>             the Jbox connections and everything on the roof “looked”
>>>             ok.  I have also check all of the connections inside the
>>>             Outback DC load center, and they look ok. Fuse replaced
>>>             3rd time and then it blew again.
>>>
>>>             Before I take all of the panels off the rack, check
>>>             panels, re-check string wiring on the roof, is there
>>>             anything else I should be checking?  Seems like that
>>>             warm wire in the Combiner box is telling me something
>>>             but I can’t figure out what...I believe this is a new
>>>             problem in the last 2-3 years but we are not 100% sure
>>>             when the problem first came up…
>>>
>>>             As always, thanks for your help/ suggestions!
>>>             Amos
>>>
>>>
>>>             <IE LOGO 150x78.jpg>
>>>
>>>                    Amos Post
>>>             Integrity Energy
>>>               W 802.763.7023
>>>                C 802.291.2188
>>>             ienergyVT.com <http://www.ienergyvt.com/>
>>>             Facebook
>>>             <https://www.facebook.com/integrityenergyllp?ref=hl>
>>>
>>>             _______________________________________________
>>>             List sponsored by Redwood Alliance
>>>
>>>             Pay optional member dues here: http://re-wrenches.org
>>>
>>>             List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>>             Change listserver email address & settings:
>>>             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>             There are two list archives for searching. When one
>>>             doesn't work, try the other:
>>>             https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>             http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>>             List rules & etiquette:
>>>             http://www.re-wrenches.org/etiquette.htm
>>>
>>>             Check out or update participant bios:
>>>             http://www.members.re-wrenches.org
>>>
>>>
>>>
>>>         -- 
>>>
>>>
>>>
>>>         Mac Lewis
>>>
>>>         *
>>>
>>>         "Yo solo sé que no sé nada." -Sócrates
>>>
>>>         *
>>>         _______________________________________________
>>>         List sponsored by Redwood Alliance
>>>
>>>         Pay optional member dues here: http://re-wrenches.org
>>>
>>>         List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>>         Change listserver email address & settings:
>>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>         There are two list archives for searching. When one doesn't
>>>         work, try the other:
>>>         https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>         http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>>         List rules & etiquette:
>>>         http://www.re-wrenches.org/etiquette.htm
>>>
>>>         Check out or update participant bios:
>>>         http://www.members.re-wrenches.org
>>>
>>>     _______________________________________________
>>>     List sponsored by Redwood Alliance
>>>
>>>     Pay optional member dues here: http://re-wrenches.org
>>>
>>>     List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>>     Change listserver email address & settings:
>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>     There are two list archives for searching. When one doesn't
>>>     work, try the other:
>>>     https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>>     List rules & etiquette:
>>>     http://www.re-wrenches.org/etiquette.htm
>>>
>>>     Check out or update participant bios:
>>>     http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, 
>>> try the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250512/9797ed0f/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: IE LOGO 150x78.jpg
Type: image/jpeg
Size: 7516 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250512/9797ed0f/attachment-0001.jpg>


More information about the RE-wrenches mailing list