[RE-wrenches] Outback MX60 Replacement
Mac Lewis
maclewis1 at gmail.com
Tue Apr 22 06:07:13 PDT 2025
Hi Jason,
One thing you might consider is an Outback FM100 with the 300Vdc input.
You can do 2 strings of 4, then combine on the roof. Typically you can
easily get that on #10 wire. This may allow the controller to show up with
the Mate. I would disable arc fault to make it work reliably.
If you can't find them, let me know off-list and I may be able to help.
Good luck!
On Mon, Apr 21, 2025 at 2:55 PM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> There are particular challenges with running new conductors to the roof,
> and I don't have 8 wires to work with, unfortunately. This is one of the
> reasons I am planning a single string at 600V
>
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
>
> On Fri, Apr 18, 2025 at 8:34 PM MDElectricSolar via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> You could swap it out with a FM-80 and do 4 strings of two modules in
>> series.
>>
>> Michael D Nelson
>> MD Electric & Solar, Inc.
>> 707-684-0064 mobile
>> 707-884-1862 office
>> www.mdelectricsolar.com
>> www.facebook.com/mdelectricandsolar
>>
>>
>> On Apr 18, 2025, at 6:40 AM, Christopher Warfel via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>
>>
>> Hi Jason, I have the same set up. These are the array and cc breakers.
>> Although we are having a power outage right now, the DC shunt is doing its
>> usual crazy reading from time to time. Chris
>>
>>
>> <2b1DSIMNoJXo0FJ2.jpg>
>>
>> On 4/18/2025 8:35 AM, Jason Szumlanski via RE-wrenches wrote:
>>
>> Hi all,
>>
>> I have a client that wants to replace a PV array that is aging and
>> hurricane damaged. It's a rather old array of unknown rating connected to a
>> MX60 via a Flexware 500 DC enclosure (48V).
>>
>> I'm planning to install eight REC 450 Alpha Pure RX in series. I'm going
>> to need a 600 volt charge controller. I'm considering a Midnite Hawk's Bay
>> unless someone has a better idea.
>>
>> The customer sent me this crude image. I can see the two inverter
>> breakers on the right. I am wondering what the two breakers on the left
>> are. I'm thinking one of these is an 80 amp breaker for the output of the
>> MX60. The other one is probably a PV input breaker of unknown rating. I
>> would need to change these to accommodate the new charge controller. The
>> Midnite Hawk's Bay 90 requires a 125A output breaker. Does anyone know if
>> there is an Outback breaker of this physical size and 125A rating to plug
>> into this DC FlexWare enclosure? For the PV input, I should be able to get
>> whatever breaker is required for this single string of PV.
>>
>> I'm all ears if there is an easier way to go about this with
>> approximately 3,600W of new PV.
>>
>> Thanks in advance!
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>>
>> Check out or update participant bios:http://www.members.re-wrenches.org
>>
>> --
>> Christopher Warfel, PE
>> ENTECH Engineering, Inc.
>> PO Box 871, Block Island, RI 02807
>> (401) 447-5773
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Mac Lewis
*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250422/a04985b8/attachment.htm>
More information about the RE-wrenches
mailing list