What voltages are you using with it for ABS? Are you running open loop? Does the battery pretend to be Pylontech or some other protocol?
Maybe the BMS is tripping from high volts, even for a brief period.
The spec does say maximum of 56V.
Most all other 16S LiFePO4 can go much higher, in theory to:
3.65 max cell voltage = 58.4
3.5 vpc is 56V
3.45 vpc = 55.2V, my favorite sweet spot
3.4 vpc = 54.4 is preferred by a few vendors.
Is the Sol-Ark on the internet so you can look at voltage charts? If so, I can look at it if you want/can share it.
Absorb time is another story.
Thank you,
Maverick
Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
• Solar Commander Remote Power
• SunFlow Systems Cathodic Protection
maverick at mavericksolar.com
512-460-9825
> On Apr 7, 2025, at 5:00 PM, Kevin Pegg via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Hello Wrenches,
>
> Has anyone seen this before? I’m dealing with a battery bank that keeps tripping out, opening the K3 contactor, randomly. I can’t find any pattern nor cause. Voltage is ok, load ok, temperature ok. It could be during the day under PV charge, or in the evening. The battery bank is paired with a SolArk 15k. Same behavior if it’s closed loop or open loop voltage-based control. SolArk tech support said it was not supported in closed loop. GSL tech support has not been useful and refuses to address the issue at hand.
>
> This is close but not exact model.
> https://www.gslenergybattery.com/20kwh-wheel-design-solar-energy-storage-battery--2048kwh-lifepo4--modular--scalable--10-year-warranty--ul-certified
>
> I wrote about this same project Dec 2024 was able to recover a frozen and 18 months abandoned deeply discharged battery bank. Capacity wise, they are fine. This site is not continually occupied; I just don’t know how to get it to the point where the system is reliable. Tempting to bypass the K3 contactor, as it still would have a secondary one for safety.
>
> Kevin Pegg
> EA Energy Alternatives Ltd.
> 37471 Hwy 16 E
> Telkwa, BC V0J 2X2
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250407/8881b649/attachment.htm>
More information about the RE-wrenches
mailing list